I was doing some run-down testing on my inverter today (for those that want to know, I got ~7.5 hours on an avg load of 900W with four 170AH lead-crystal batteries - yes I fully discharged them for this test).
However, I also grabbed my oscilloscope and measured the switchover times (from Eskom to inverter and back). Also measured the delay time the UPS includes before it switches back to Eskom.
Now, in UPS mode, the manual quotes 10ms switchover, but here are my results (have a look at the delta-T values in the top-left corner):
Switchover from Utility to Inverter
Fallback from Inverter to Utility
As you can see, both times are 28ms. Longer than what the manual quotes, but it seems good enough for all my electronic kit to survive the switchover time. Note the slight ramp-up in voltage when the Inverter gets going.
The inverter introduces a 6 second delay before it switches back to mains after Utility power is back. Presumably (and sensibly) this is done to wait for the Utility power to stabilise, as I've seen some horrible spiking on the mainline when the power comes back to 20,000 houses all at the same time:
I didn't do any tests in APL mode (really don't see the need to). I used a 28V isolated step-down transformer to measure the output (hence the slightly distorted sine wave). The inverter sine wave output is 100% pure.
What is also interesting is that it appears that there is some sort of phase-sync going on (the Utility waveform is in phase with the inverter output). I repeated the test 3 times just to be sure - maybe I was just lucky in that the inverter wave clock happened to be in sync with Eskom.
--deckert
I was doing some run-down testing on my inverter today (for those that want to know, I got ~7.5 hours on an avg load of 900W with four 170AH lead-crystal batteries - yes I fully discharged them for this test).
However, I also grabbed my oscilloscope and measured the switchover times (from Eskom to inverter and back). Also measured the delay time the UPS includes before it switches back to Eskom.
Now, in UPS mode, the manual quotes 10ms switchover, but here are my results (have a look at the delta-T values in the top-left corner):
Switchover from Utility to Inverter
Fallback from Inverter to Utility
As you can see, both times are 28ms. Longer than what the manual quotes, but it seems good enough for all my electronic kit to survive the switchover time. Note the slight ramp-up in voltage when the Inverter gets going.
The inverter introduces a 6 second delay before it switches back to mains after Utility power is back. Presumably (and sensibly) this is done to wait for the Utility power to stabilise, as I've seen some horrible spiking on the mainline when the power comes back to 20,000 houses all at the same time:
I didn't do any tests in APL mode (really don't see the need to). I used a 28V isolated step-down transformer to measure the output (hence the slightly distorted sine wave). The inverter sine wave output is 100% pure.
What is also interesting is that it appears that there is some sort of phase-sync going on (the Utility waveform is in phase with the inverter output). I repeated the test 3 times just to be sure - maybe I was just lucky in that the inverter wave clock happened to be in sync with Eskom.
--deckert