Step 1:
Everything you want on generator power needs to be on one phase.
What this involves:
This may involve moving some of your electrical components to other phases, the rule imposed by SANS is the phases must be balanced as realistically as possible.
For some installations this can mean you need an extra RCD (or "earth leakage" as SA likes to call them)
The Eskom supply, which runs to your Eskom contactor should
NOT be wired via an RCD. The RCD is added
AFTER the contactor. It should be on a
MCB before the contactor however, rated to the current capacity of the wiring.
Step 2:
Depends on the installer, but I would use a 2p or 3p contactor (p = pole) x2 with mechanical interlock
One contactor coil is powered by Eskom power, the other contactor is powered by generator. You also need a 1P auxiliary to prevent the generator contactor from turning on if the generator & Eskom are active at the same time.
Most contactors come with an auxiliary, almost every mechanical interlock unit also comes with one.
Generator output run to the generator contactor, should have a
MCB before the contactor rated to the current capability of the *CABLE* not your generator capacity.
Step 3:
Wire the two contactor outputs to a single
MCB (double pole) +
RCD, and from there wire all the circuit breaker
MCBs to that RCD.
At this point the automatic change over is complete.
Summary:
Eskom Power -> Double Pole Breaker -> Contactor ->
Backup Power Double Pole Breaker -> RCD
Generator Power -> Double Pole Breaker -> Contactor ->
Backup Power Double Pole Breaker -> RCD
Highlighted sections are shared.
Shared section:
Backup Power Double Pole Breaker -> RCD -> Single Pole breakers (Lights for example, Plugs, etc.)
In each case the breakers are rated for the
CABLE. Your generator should have its own ability to cut off in the event of over current. The breakers are there to protect the wires, not your generator (so you may need a circuit breaker just for the generator)
Technically you can make the Backup Power Double Pole Breaker rated to your generator output! That would probably be your wisest choice.
Step 4:
Depends on the generator, you need to wire the generator to auto-start during a power outage.
This is not a *must* but will require you start the generator manually.
Can think of a way to do this with a relay, but honestly it really depends how the generator starts. Like is it a push button, let go and it starts itself. Is it a push and hold until it starts.
Both are trivial to make auto-start for with a few relays.
Also consider the housing of your generator, petrol levels, etc. You may not want auto-start.