At 5400W/48V you have 112 Amps, good luck finding a charge controller that can do that. You probably going to need 2 charge controllers.
Assuming he can put 3 in a string for 150v max (what most MPPT controllers take as max these days) - which is of course a big assumption the Voc for 24v panels may be too high for that.
And assuming 15A per string (bit of a thumbsuck), that is a 90A controller roughly, which is towards the higher end of whats on the market but is available, two 50A controllers that work together is perhaps a better option though.
Of course the above is all just thumb sucking, without the actual panel specs with the Voc and max amps etc.
The main question is, are the batteries actually big enough to warrant that much juice, or should he rather either have more batteries or make some of panels rather just go straight to the inverter.
Sorry how do you get to a total of 90A? 300W * 18 = 5400W. You need a controller that can output at ~48V. Ie 5400/48 = 112.5A. Assuming no losses.
Ok what would you suggest I do here is my load profile I have 30 led 3w ligts total, 1.1kw borehole pump that wil run 20min per day, 2 garage motors, 1 gate motor 2 selfone chargers, microwave 800w, double door fridge freeze A+++ rating box deepreeze, 2 dstv decoders 1x 50inch led 1 x 32 inch led, 300w woodsaw for about 1 hour a day, ligts I was told to run off 12v, the inverter I am using is a devel sps 6000w with 45A mppt charger and I will have another mppt 100A charger, the batteries is 180ah monbat gel vrla batteries, if need be I will change some of this system
what about geysers?