Modern engines are online in seconds
No, they have to start and then warm up before load can be applied. Sudden load on a cold diesel running at generation speed will drastically reduce it's life. Modern software will wait for the diesel to be warm and increase the speed gradually to generation speed depending on temperature.
Once at generation speed (Essential because the frequency of the electricity is dependent on the speed of the generator) the software will synchronise the phases of the generator with the power being supplied and then switch it on line. An unsynchronised generator switched on line can cause catastrophic damage to the diesel engine or generator.
This can be done manually too but requires experience.