Does the amount of cells in a panel matter?

Wrath of Khan

Senior Member
Joined
May 4, 2015
Messages
847
Just a quick question:

Does the amount of cells in a solar panel matter to your inverter?
Reason being my inverter says, "adapted to 60 & 72 cell PV panels"
The operating voltage range is 16-60v

The panel I am looking at is 380w / Voc 42v / 120 cells...
 

Speedster

Honorary Master
Joined
May 2, 2006
Messages
21,675
Just a quick question:

Does the amount of cells in a solar panel matter to your inverter?
Reason being my inverter says, "adapted to 60 & 72 cell PV panels"
The operating voltage range is 16-60v

The panel I am looking at is 380w / Voc 42v / 120 cells...
120 cells are actually 60 half cells. Number of cells doesn't really matter for any practical purposes, as long as your string voltage is within the mppt spec.
 

itareanlnotani

Executive Member
Joined
Sep 14, 2008
Messages
6,760
Panel Voltage will be higher with more cells.

You must have a pretty low end inverter if thats one of the sales points.

Which inverter is it? Or is it just a pwm or mppt unit?
 

Wrath of Khan

Senior Member
Joined
May 4, 2015
Messages
847
Panel Voltage will be higher with more cells.

You must have a pretty low end inverter if thats one of the sales points.

Which inverter is it? Or is it just a pwm or mppt unit?

its a micro inverter, so will attach 4x 380w panels to the inverter
 

Attachments

  • hoymiles 1200w.pdf
    1.1 MB · Views: 10

itareanlnotani

Executive Member
Joined
Sep 14, 2008
Messages
6,760
its a micro inverter, so will attach 4x 380w panels to the inverter
At, that makes sense then, as its a micro inverter. You need to be very careful speccing out the panels for this.
Lower watt panels only really, as they haven't kept up with the times.


60v/10.5A max. Check VOC carefully for your panels, and add 10% or 15% on top of VOC as that can be exceeded.

Amps can generally be clipped, but voltage going over means magic smoke go boom boom, and device unhappy chappy.

So. Be. Careful.
 

Wrath of Khan

Senior Member
Joined
May 4, 2015
Messages
847
At, that makes sense then, as its a micro inverter. You need to be very careful speccing out the panels for this.
Lower watt panels only really, as they haven't kept up with the times.


60v/10.5A max. Check VOC carefully for your panels, and add 10% or 15% on top of VOC as that can be exceeded.

Amps can generally be clipped, but voltage going over means magic smoke go boom boom, and device unhappy chappy.

So. Be. Careful.

I wish they would be more specific in their paperwork on these inverters.
Ok so this inverter says it can take 4x 380w panels

The panel Voc = 41.6v
Short circuit amps = 11.47a
Max power amps = 10.93a

Inverter max operating voltage 16-60v (I'm guessing that's the Voc)
Maximum Input Current = 10.5a (but amps aren't critical as I believe they get clipped or something)

What they don't say in the paperwork is that I'm sure that's per connection right?! (which their are 4 --> for the 4 panels) If I take 41.6v out of a max 60v allowed, then I'm only at 69%, so should be perfect :)

So all the above will be per panel, and I attach 4 panels to the inverter. I guess the inverter connections are obviously in parallel and not series otherwise the voltage would pop it.
 

itareanlnotani

Executive Member
Joined
Sep 14, 2008
Messages
6,760
I wish they would be more specific in their paperwork on these inverters.
Ok so this inverter says it can take 4x 380w panels

The panel Voc = 41.6v
Short circuit amps = 11.47a
Max power amps = 10.93a

Inverter max operating voltage 16-60v (I'm guessing that's the Voc)
Maximum Input Current = 10.5a (but amps aren't critical as I believe they get clipped or something)

What they don't say in the paperwork is that I'm sure that's per connection right?! (which their are 4 --> for the 4 panels) If I take 41.6v out of a max 60v allowed, then I'm only at 69%, so should be perfect :)

So all the above will be per panel, and I attach 4 panels to the inverter. I guess the inverter connections are obviously in parallel and not series otherwise the voltage would pop it.
Looking at the unit, it has 4 paired connectors, so would likely be in the center of your 4 panel mounting.
Each connector directly to a panel, so no parallel or serial setup on the panels themselves.

1657796229692.png

Screen Shot 2022-07-14 at 13.02.50.png




Any particular reason you're going with a micro inverter?

You just want AC supplemented?
This won't help with load shedding, only with supplementing existing grid - i.e. to reduce your bill.



Their website says that the MI-1200 can do 11.5A max @ 60V


Datasheet - https://www.hoymiles.com/wp-content/uploads/2022/06/User-Manual_HME-12001500-AU_V202203.pdf
 
Last edited:

Wrath of Khan

Senior Member
Joined
May 4, 2015
Messages
847
Looking at the unit, it has 4 paired connectors, so would likely be in the center of your 4 panel mounting.
Each connector directly to a panel, so no parallel or serial setup on the panels themselves.

View attachment 1346584

View attachment 1346612




Any particular reason you're going with a micro inverter?

You just want AC supplemented?
This won't help with load shedding, only with supplementing existing grid - i.e. to reduce your bill.



Their website says that the MI-1200 can do 11.5A max @ 60V


Datasheet - https://www.hoymiles.com/wp-content/uploads/2022/06/User-Manual_HME-12001500-AU_V202203.pdf

Ja I have a lot of shading on my roof from the neighbours tree... I was just about to get a "normal" hybrid inverter and then found out about the shading issue on 1 panel which would then affect them all. All the info I found was that on a micro-inverter system shading is not an issue as it only affects that particular panel. And the wiring for the AC side of things is straight forward, no DC at all :)

Oh and yeah not for load-shedding, it's just to reduce my electricity bill. I have big freezers that runs all the time so my elec is around R5k a month. If I can get solar during the day time then that should reduce my bill "hopefully"

I can't afford batteries etc, maybe one day I'll save up for a big battery cart that I can then plug directly into a DB board and then switchover at night when there's a power failure. But I'm ok for now :)
 

wingnut771

Honorary Master
Joined
Feb 15, 2011
Messages
28,144
Ja I have a lot of shading on my roof from the neighbours tree... I was just about to get a "normal" hybrid inverter and then found out about the shading issue on 1 panel which would then affect them all. All the info I found was that on a micro-inverter system shading is not an issue as it only affects that particular panel. And the wiring for the AC side of things is straight forward, no DC at all :)

Oh and yeah not for load-shedding, it's just to reduce my electricity bill. I have big freezers that runs all the time so my elec is around R5k a month. If I can get solar during the day time then that should reduce my bill "hopefully"

I can't afford batteries etc, maybe one day I'll save up for a big battery cart that I can then plug directly into a DB board and then switchover at night when there's a power failure. But I'm ok for now :)
Do you have a spinning disk meter?
 