Oh, the generator, I'll explain as best I can our current setup. as the generator was here when we moved in..
Main grid supply comes in from the street, DB outside with smart meter and a what I presume is 60A CB. There is another DB on the side of teh house with another 60A CB and this feeds to the generator control box. The generator control box then has a grid only feed and generator feed to our main DB in the house. The main DB then has a feed to our inverter with the inverter CT clamp on the grid only feed from the generator controller box to the main DB. So at the moment the generator controller can pick up there is no grid feed, if it is set to Auto it will start the generator and stop it when grid returns. The inverter picks up that there is no grid feed from the main DB and via the CT clamp. If I run the generator, the inverter picks up that there is 'grid' from the main DB but the CT clamp picks up nothing as the grid only feed from the generator controller box to the main DB is dead.
So, I need to change this so that either the generator powers the inverter via the Gen port or maybe the CT clamp is over both the generator and grid only feeds, to enable us to use the generator with the inverter.