@Gtx Gaming
What is the cable thickness for the battery? Assuming you have a 3kW 24V (3000W/24=125A) inverter, using this tool:
1666413280948.png

Then again, the hubble is limited to 100A so would probably cut out before you can max out the inverter. Even with 100A it's still recommending 25mm² cable.
1666413411938.png
I would also add a 150A fuse to protect the cable from fire in case the BMS fails.
 
@Gtx Gaming
What is the cable thickness for the battery? Assuming you have a 3kW 24V (3000W/24=125A) inverter, using this tool:
View attachment 1406543

Then again, the hubble is limited to 100A so would probably cut out before you can max out the inverter. Even with 100A it's still recommending 25mm² cable.
View attachment 1406545
I would also add a 150A fuse to protect the cable from fire in case the BMS fails.
I also thought the cable looks dodgy.
 
Just made toast on battery power, and Noticed the Lobo ramps up the fan when outputting higher power 900w in my case.
Most do that :) what batteries do you have?
 
Currently, 34 X 7ah LA batteries wired up for 24v.
Waiting for my 24v 100ah LFP from Scott.
That is a lot of batteries to try maintain though I guess it brings almost 240ah
 
Can I replace my two 18-month-old gel batteries kicking the can with this on the Mecer?

 
Can I replace my two 18-month-old gel batteries kicking the can with this on the Mecer?

Technically yes
 
Can I replace my two 18-month-old gel batteries kicking the can with this on the Mecer?

If you have the 12V Mecer then go for it, if you have the 24V Mecer its overkill to wire 2 of these in series, because you won't be able to charge them fast enough to make use of 400Ah capacity
 
If you have the 12V Mecer then go for it, if you have the 24V Mecer its overkill to wire 2 of these in series, because you won't be able to charge them fast enough to make use of 400Ah capacity
He would also not be able to discharge them fast enough, I don't think that's much of a problem, overkill, yes.
 