I can't remember the connection layout in each string, will have to ask him on Monday again, but each string is 12 panels. Apart from the breaker issue the guy's work is top-notch and has done entire hotels with up to 200 kW, so I'm not concerned about his wiring.
12 panels on a string? Wont that exceed the MPPT Voltage? @RonSwanson

Edit: Attaching image panel spec sheet

1637326769201.png

Cutting it a bit close there?
 

semaphore

Honorary Master
Joined
Nov 13, 2007
Messages
15,206
The voltage agree's with my statement. Current is relative to the conditions. If it was 12 x 41V = 492V. So you have 2 parallel strings on each MPPT.
Yeah, I remember something about them doing series and parallel arrangments, I'll be honest I wasn't really paying attention.
 

DuracellBunny

Well-Known Member
Joined
Apr 26, 2016
Messages
403
Looks like a double up on strings there, Voltage not matching 12 panel for 1 string. So as the day progresses and some nice sunny sun must be exceeding the amps and tripping

Edit - Perhaps get them to come back, the Inverter you have would be an 18A controller so if its tripping on 16A then it can surely go higher than the 18A, Dont think this is good for the MPPT controller

Correct myself to the Above, Sunsynks new firmware allows to 22A
 
Last edited:

semaphore

Honorary Master
Joined
Nov 13, 2007
Messages
15,206
Edit - Perhaps get them to come back, the Inverter you have would be an 18A controller so if its tripping on 16A then it can surely go higher than the 18A, Dont think this is good for the MPPT controller
The inverter I have is 22A (8kw).

@AchmatK Correct me if I'm wrong but the inverter auto clips excessive amps?
 

RonSwanson

Honorary Master
Joined
May 21, 2018
Messages
15,327
The inverter I have is 22A (8kw).

@AchmatK Correct me if I'm wrong but the inverter auto clips excessive amps?
Newer versions of it, yes. If you give me your serial # I can ask...
If you give me the model # of your panels I can also check it out for you.
 

RonSwanson

Honorary Master
Joined
May 21, 2018
Messages
15,327
lr4-72hph-455m

PM'd inverter details
OK so the 8K which you have has an MPPT capable of 22A.
Your panels are probably (I am guessing here) in two paralleled strings, 6 in series, 2 in parallel that means 297V and 21.84A max. So all cool as far as the MPPT is concerned
 

semaphore

Honorary Master
Joined
Nov 13, 2007
Messages
15,206
OK so the 8K which you have has an MPPT capable of 22A.
Your panels are probably (I am guessing here) in two paralleled strings, 6 in series, 2 in parallel that means 297V and 21.84A max. So all cool as far as the MPPT is concerned
Cool, if they had to overshoot they'd just be clipped due to the model I have?
 

RonSwanson

Honorary Master
Joined
May 21, 2018
Messages
15,327
Cool, if they had to overshoot they'd just be clipped due to the model I have?
The amps yes, it's easy to reduce that, volts are another story. You could probably put another 4-5 panels per MPPT before you even get close to 450V.
 

maxxis

Expert Member
Joined
Jul 26, 2007
Messages
1,601
5kw vs 8kw for me was peace of mind using without thinking. 5kw you need to manage loads carefully
This is exactly where my mind is right now.

1 battery and 8kw and add second battery later

Or second battery now with 5kw and manage it. We are only two people in the house.
 

Snyper564

Honorary Master
Joined
Oct 1, 2008
Messages
15,343
This is exactly where my mind is right now.

1 battery and 8kw and add second battery later

Or second battery now with 5kw and manage it. We are only two people in the house.
I can tell you go with the 8kw and 1 battery now. Then save for the second battery.

My wife doesnt think twice and we have no split load everything is on it.

We had a braai on Sunday and the kettle, oven and induction stove was on no issue.

8Kw provides a bit of future proofing and remember your battery can only charge as fast as you can put power though it - so the 8kw will charge your battery quicker to full capacity
 