Is it the MCB or the ELB that is tripping? What is it rated at?Yeah, nothing. Fml must be an earth leak somewhere. Happened twice yesterday and once today.
MCB = Main Circuit Breaker? If so yes.Is it the MCB or the ELB that is tripping? What is it rated at?
Sometimes there might be something exposed to water causing a trip happened to us years ago, with all the rain something that usually isn't wet is wet.Yeah, nothing. Fml must be an earth leak somewhere. Happened twice yesterday and once today.
Yeah, thought of that but then should be a more consistent trip, happens very infrequently.Sometimes there might be something exposed to water causing a trip happened to us years ago, with all the rain something that usually isn't wet is wet.
MCB = Miniature Circuit Breaker. In other words on your essentials DB? Then it's a fault with the house wiring / plugs / switches / appliances. What is the MCB rated at?MCB = Main Circuit Breaker? If so yes.
If it is the main breaker tripping that means an overload? Mine has also done this at random times, I think the breaker is in need of replacement. It has tripped when a few appliances were switched on together, but should still be below the rating of the breaker.Yeah, thought of that but then should be a more consistent trip, happens very infrequently.
63A, it's only started tripping since the solar was installed. No trips at all prior.MCB = Miniature Circuit Breaker. In other words on your essentials DB? Then it's a fault with the house wiring / plugs / switches / appliances. What is the MCB rated at?
Yeah was thinking this as well, what brand would you suggest?If it is the main breaker tripping that means an overload? Mine has also done this at random times, I think the breaker is in need of replacement. It has tripped when a few appliances were switched on together, but should still be below the rating of the breaker.
63 amps is alot of current, it could be faulty.63A, it's only started tripping since the solar was installed. No trips at all prior.
This63 amps is alot of current, it could be faulty.
Elcb
So you think it could be faulty?Elcb
Okay, well the solar guy is coming tomorrow and hopefully he can try isolate where the issue is.That the earth leakages.
It's not Tripping due to an overload
Nothing like a solar installation to highlight hidden wiring issues.Okay, well the solar guy is coming tomorrow and hopefully he can try isolate where the issue is.
Correct, just asking, I know that mine were done.Panels are earth for lighting protection.
Not for earth leakage protection