Swa
- May 4, 2012
Current step down transformers used in all your DC appliances wastes even more power. You're also completely missing the point of converting to DC.Dude it steps the voltage from 12V to a higher one to charge laptops.
Output: DC 15/16/18/19/20V 4A DC 22/24V 3.3A 80W Max
So you're back to wasting power with DC-DC boost converters.
The point is to be self sufficient and not rely on an external utility to supply power for essential appliances. I guess you're quite happy though to put all your eggs in a basket that will in one months time be technically bankrupt. Those with two separate supplies will at least be able to use some appliances when things go belly up. You probably missed this part as well but your DC appliances are already using two standards as they convert from the wall supply to DC.Then what's the point?
I don't see the logic about having to have two separate standards for appliances. At least at the moment everything runs off 220-240V 50Hz AC.
A car charger IS 12V.But that is still not 12 V
Again not the point but to counter your argument you are already using an inefficient means of conversion from AC for all your DC appliances. Running AC from a DC source through an inverter is even less efficient. Switched mode power supplies are more efficient than your current transformer based step-down tech you are using in almost every DC appliance.Yes - and it contains a DC-DC converter that is creating a higher voltage. As per the specs: "Output: DC 15/16/18/19/20V 4A DC 22/24V 3.3A 80W Max"
DC-DC converters are at least as inefficient as AC-DC switch-mode power supplies - often far worse.
And you are grasping at straws. The voltage drop at source is not due to resistance but rather that it supplies power as a factor of voltage and current commonly known as wattage. Drawing more current from a supply where this is limited therefor results in a voltage drop. This typically doesn't affect lead-acid batteries though as they can usually supply several hundred watts.Your lack of knowledge and arrogance is growing tiresome.
Voltage drop is due to resistance. There is some resistance in the source (power supply), some in the cable and normally the majority of the resistance is in the load. The biggest reticulation challenge however is the resistance in the cable. Voltage drop is highest when the current in the cable is high. This will happen when trying to trying to carry too much power at too low a voltage. The way to combat that is to reduce the current - but if you still need a significant amount of power then you need to raise the voltage.
12 V is too low to reticulate usefully for more than about 20 metres unless you have extremely thick and expensive cabling. The only reason 12 V is popular is due to its use in cars and thus with cheap lead acid batteries and cigarette lighter accessories. Most industrial and business grade DC systems use either 24 V or 48 V.
Voltage drop in a wire is negligible for small distances like house wiring and it isn't unique to DC. AC systems also suffer from this and even more so due to the skin effect. Since this is unique to AC systems DC current can flow through the entire diameter of a wire thereby decreasing the resistance and voltage drop.
