Thread: Need help on SP24 Solar geyser controller

  1. #1
    Super Grandmaster isie's Avatar
    Join Date
    Jan 2010
    Location
    Second star to the right and straight on 'til morning
    Posts
    7,935

    Default Need help on SP24 Solar geyser controller

    Hi All
    Does anyone else have a Sp24 Solar geyser controller looks like this.
    i found the manual and a youtube video on it but it doesn't give much info on what setting is what.

    Name:  solar-water-heater-controller-intelligent-SP24-for-split-pressure-system-2-years-warranty-500set.jpg
Views: 165
Size:  20.8 KB

    I want the solar to warm it up over 60c but electric backup to be only like max 50c so that way the electric doesnt use alot of power and don't need to worry about Legionella if the Solar takes care of that?
    also any other tips the controller doesn't seem very smart as It looks like it works based on a time based for both solar and Electric back up but not purely temp based
    Attached Images  
    Some times the internet is so slow, it would be faster to just fly to Google's headquarters and ask them this $h1t in person.!

  2. #2
    Senior Member
    Join Date
    Mar 2004
    Location
    South Africa.
    Posts
    303

    Default

    Isie,

    It should work strait out of the box. Delta Temp is 7 or 8 deg. Just make sure T1 = temp probe in collector, and T2 is temp probe in geyser. T1 should be a 10K probe , and T2 a 1K probe, else your readings will be off. The pump signal - the arrow pointing upwards on the left of the LCD screen, should start to flash when delta temp is reached, and switch off when T1 is close to T2.
    mylinuxbox> Iburst -r linuxbox> Telkom -T +H
    mylinuxbox> Ibust linuxbox> Helkom
    mynewlinuxbox> Neotel -e
    mynewlinuxbox> Notel

  3. #3
    Super Grandmaster isie's Avatar
    Join Date
    Jan 2010
    Location
    Second star to the right and straight on 'til morning
    Posts
    7,935

    Default

    Quote Originally Posted by SideWinder View Post
    Isie,

    It should work strait out of the box. Delta Temp is 7 or 8 deg. Just make sure T1 = temp probe in collector, and T2 is temp probe in geyser. T1 should be a 10K probe , and T2 a 1K probe, else your readings will be off. The pump signal - the arrow pointing upwards on the left of the LCD screen, should start to flash when delta temp is reached, and switch off when T1 is close to T2.
    thanks man, thats how its set up , i just need to check what sensors were used in each. so far i had to only replace the sensor on the collector
    But so far looks like it switches off when the temps are close, just like I said doesn't seem very intelligent
    Some times the internet is so slow, it would be faster to just fly to Google's headquarters and ask them this $h1t in person.!

  4. #4
    Senior Member
    Join Date
    Mar 2004
    Location
    South Africa.
    Posts
    303

    Default

    Yes, I think the unit switches off when the temp of both are close. There should be a setting for this. DELTA ON & DELTA OFF

    BTW, I think I got the two probe types mixed up.

    T1 (the one in the collector) must be a PT1000 one, T2-T5 is the NTC10k type.
    mylinuxbox> Iburst -r linuxbox> Telkom -T +H
    mylinuxbox> Ibust linuxbox> Helkom
    mynewlinuxbox> Neotel -e
    mynewlinuxbox> Notel

  5. #5
    Super Grandmaster isie's Avatar
    Join Date
    Jan 2010
    Location
    Second star to the right and straight on 'til morning
    Posts
    7,935

    Default

    Quote Originally Posted by SideWinder View Post
    Yes, I think the unit switches off when the temp of both are close. There should be a setting for this. DELTA ON & DELTA OFF

    BTW, I think I got the two probe types mixed up.

    T1 (the one in the collector) must be a PT1000 one, T2-T5 is the NTC10k type.
    yep collector has the pt1000 and the t1 and t2 have the ntc type
    Some times the internet is so slow, it would be faster to just fly to Google's headquarters and ask them this $h1t in person.!

+ Reply to Thread

Similar Threads

  1. Solar Panels instead of Solar Geyser?
    By Zoomzoom in forum Eskom and Electricity: Load Shedding, Generators, UPS, Alternative Power
    Replies: 37
    Last Post: 03-11-2016, 09:03 PM
  2. Solar geyser vs Heatpump Geyser vs Gas Geyser
    By killkom in forum Off Topic
    Replies: 161
    Last Post: 21-07-2016, 11:46 AM
  3. Solar Geyser
    By JIMMYtheSKULL in forum Off Topic
    Replies: 16
    Last Post: 20-01-2015, 10:58 AM
  4. Solar Geyser
    By nadeem_k in forum Eskom and Electricity: Load Shedding, Generators, UPS, Alternative Power
    Replies: 7
    Last Post: 02-04-2014, 09:28 AM
  5. Solar Geyser
    By catman37 in forum Off Topic
    Replies: 14
    Last Post: 08-11-2012, 06:55 AM

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •