    Default Repairing Mecer ME-850 UPS

    My Mecer ME-850 UPS stopped working after many years of service. When I switch it on, nothing happens - no lights on the front panel. When I disconnect & reconnect mains supply, no relay clicking noise. Can anyone suggest where I can find the circuit diagram or service manual for this UPS?
    Thank you

  2. #2
    Senior Member
    Join Date
    Jul 2011
    Posts
    143
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Default

    Not sure if the Mecer is a rebranded APC but this is what i have.
    http://www.heime.org/Lists/Posts/Post.aspx?ID=1

  3. #3
    Active Member
    Join Date
    Sep 2013
    Location
    Stellenbosch
    Posts
    95
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Default

    Thanks Dirk, but the circuit shown on the website you've emailed confirms my Mecer is not a rebranded APC. I stumbled on this:

    https://www.ebay.ie/itm/new-ups-boar...-/252957604658

    which is exactly the board I have. Seems the Mecer is a rebrand of Advice PRV850 UPS sold by Advice, a company based in Israel...

  4. #4
    Grandmaster
    Join Date
    Aug 2008
    Posts
    1,675
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Default

    Did you check if your batteries have enough voltage to power it up?

  5. #5
    Active Member
    Join Date
    Sep 2013
    Location
    Stellenbosch
    Posts
    95
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Default

    Quote Originally Posted by The_Traveller View Post
    Did you check if your batteries have enough voltage to power it up?
    The battery sits at around 10V, so its probably dead. However, surely if one switches on the UPS at least the red mains light should come on? All lights are dead on the front panel when switching it on.

  6. #6
    Active Member
    Join Date
    Sep 2013
    Location
    Stellenbosch
    Posts
    95
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Default

    Quote Originally Posted by CommsPlayer View Post
    The battery sits at around 10V, so its probably dead. However, surely if one switches on the UPS at least the red mains light should come on? All lights are dead on the front panel when switching it on.
    Mmm...according to the user manual, no lit lights on the front panel could mean a dead battery...

    https://technowave.co.za/img/cms/Mecer/Mecer%20UPS/650-2000VA%20Mecer%20UPS.pdf

  7. #7
    Active Member
    Join Date
    Sep 2013
    Location
    Stellenbosch
    Posts
    95
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Default

    ..and then I took out the battery, the side that faced the transformer is cracked and bulging outwards! I guess I'd need to replace it, hopefully UPS functionality will be restored then.
    Attached Images  

+ Reply to Thread

Similar Threads

  1. Repairing BB Bold
    By blunomore in forum Blackberry
    Replies: 13
    Last Post: 13-08-2013, 12:37 AM
  2. Repairing .mov files?
    By Arzy in forum Software
    Replies: 0
    Last Post: 21-09-2009, 09:14 AM
  3. Repairing scratched dvd's
    By blue-eye-boy in forum Off Topic
    Replies: 6
    Last Post: 23-12-2007, 12:19 AM
  4. Mecer WAP 404 Mecer Wireless 802.11b/g/Turbo g Access point
    By rakeshb in forum ADSL and VDSL Discussions
    Replies: 2
    Last Post: 25-08-2007, 08:57 AM
  5. Repairing a Scratched Cd
    By Telkomisaloser in forum PC Hardware and Gadgets
    Replies: 18
    Last Post: 10-05-2006, 06:58 PM

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •