Hi AMJK
That is 400Ah.
Rule for batteries for series connection add voltage so 12V + 12V +12V +12V equals a 48V battery bank of 100Ah.
You have 4 strings in parallel now voltage stays the same and you add Ah = 400Ah.
HI Virgil
Mine is exposed but in the corner. The lady I employ to do domestic chores is ironing at the moment and the shunt is not even warm to the touch. The shunt is safe unless you cats start chewing cables etc. The reason why it made from plates like that is not for cooling but for accuracy...
Morning Virgil
Nothing to worry about the fans are there to protect the unit. Counter-intuitively they blow down whilst hot air rises so that is a design flaw. I would not run the inverter at more than 75-80% of capacity for any length of time. 3kW is fine but heat kills components and the...
Hi Virgil
Look at Victon's website they have a map with all the Victron agents. If you are in the Western Cape the Exsolar seem a good supplier but shop around. I got my BMV 702 from Telecom Techniques in PE.
Chris
Very similar to my setup. The only difference is that I have 12 x 250W Yingli panels.
Program 1 probably SOL or SBU you decide what suits you best.
Program 2 20A (so that you stay below C10 charging rate.
Program 3 UPS and if you grid power is of not good enough quality Appliance
Program 4...
Why not a RCCB that detects any difference in current flow between live and the neutral. In a perfect circuit they should be the same. Then you do not have the hassles with bonded earths etc. If safety is your primary concern then a RCCB is the safest thing I can think of. The hassle is that...
Edmundp in this thread identified that if you have your low battery cut-off set to anything other than the default (42V in a 48 V system or 21V in 24V system) the SOC goes for a ball of ...... The SOC is much better but not accurate with the default low battery cut-off, a Victron BMV battery...
Hi treeman
Those panels are dedicated to the geyser. My panels can power washing and ironing on Tuesdays and Thursdays and heat water the other days of the week.
Hi Rudi
I am very happy with my installation - been up and running for about 3 weeks. Draw down overnight is between 35 and 50 Ah. Produces 14-15 kWh on a sunny day. On the days that there is no washing or ironing the batteries are charged by 10:30 am. I have found a geyser that was equipped...
I bought it from the Victron supplier in PE Telecom Techniques I think they call themselves. I bought the 702 (more expensive model) since I was keen to be able to measure mid-point voltage on a 48V battery bank. I paid R2622.00 vat incl This compared favourably with other quotes and the price...
I have bought a Victron battery monitor. Spend the extra money and get a 702 and monitor the mid-point voltage of your battery bank. The Axpert unfortunately is like driving a vehicle with faulty fuel gauge. It is at some point going to let you down.
Edmundp in this thread posted that if you...
Hi Jackie
One should be using VOC + temperature co-efficient for your Max voltage and Isc for max current (A). These are the maximum possible figures you could see. You design you system round this in terms of cable size, fusing and inverter input (safety). You are unlikely to get anywhere near...
Thanks! That was a revelation! I am waiting for a Victron monitor as I don't like the way the Axpert makes no sense at times.
Do you have a blog of your experiences?