I don't think that solar is really the best way to beat load shedding, expensive and all. But I must say when I first was looking into an inverter backup for load shedding I realised how expensive a simple charger is. If you don't have a built-in charger on your inverter/ups system, a solar...
You could, but it'd be a real las to wire. Because the 3kVa inverters can't be paralleled (sync the waveforms) you have to run them separately as you say. You can draw the power from the same batteries but I'm not sure how much the internal chargers would like competing with each other. Then on...
The idea is that you distribute the inter-battery connection's resistance to prevent the connection's wire/bar resistance (no matter how small) from making one battery deliver more current than the other. It's recommended practice, whether you choose to do it or not is totally up to you.
Hi, typically with a deep cycle battery you don't want to discharge past 50% so 2x102x0.5=102ah worth of use, multiply by 12 = 1224Wh ie. you can run something which draws 1224 watts for an hour, or 612 watts for 2 hours etc.
you'll probably average a load of about 600 watts (lights, tv etc) so...
The problem with a parallel set up is that one battery will tend to deliver the current over the other and worse since no two batteries are the same one might actually discharge the other. If you do go this route link the batteries +ve to +ve and -ve to -ve but make sure that you take your load...
For such a small fluctuation I'm not sure I'd even worry about the microwave and fridges. To just clarify my other post because I wasn't being very accurate. You get different types of loads, resistive, inductive and capactive. Purely resistive load (like heaters, geysers and kettles etc) won't...
It really depends on what you are powering. The utility grid typically fluctuates -+0.5Hz. Most electronics will be fine with small fluctuations but increasing the frequency can have a similar effect to increasing the voltage. I would say for fluctuations of about 2Hz it's nothing to worry...
Hi Greg,
My understanding (which may be wrong : is similar to an electric fence, if the current leaks to earth/ground through you or an object, it is actually forming a conductor via the earth/ground to the neutral which is connected to the ground either at the utility station or through your...
Hi Greg,
I think it's probably unnecessary for the changeover switch, I just see the inverter breaking and the missus without lights while eskom is actually providing power going down really well :p. But you're right that it shouldn't take very long to just bypass the inverter.
Have you...
Does anybody know if these units have a true neutral? Such that you can tie the ground and earth when wiring to your DB Board?
I've ordered one of these units and my plan is to isolate the house light circuits from the eskom supply with a changeover switch and a separate earth leakage breaker...