Recent content by Devinc

  1. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Total wattage being used is less than 300W normal usage. The unit is constantly plugged in. I am eskom grid and not city of Cape Town. I get loadshedding very often currently 4 times a day. It is very easily gone through its charge cycles.
  2. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Hi, I bought gel batteries to hold me over. I'm looking into 5kw hybrid inverter (luxpower or Sunsynk) that will be wired into the BD and have the option for solar. I run my business from home and can't afford to be offline this often and I can't justify having to replace batteries every 12...
  3. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Hi, Thank you. I have ordered new batteries which arrive next week. I was hoping I could of saved at least one of these batteries. Is it worth trying to trickle charge them?
  4. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Hi, For the stress test I added a lot more devices then I would ever use. The point of getting it to 50% was to see if the batteries voltage dropped under load. My usual load never exceeds 25%. As mentioned usually only run the tv, soundbar and router. When working from home it is only...
  5. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Hi, I'm currently in loadshedding. I put a much higher load through the system then I usually do. Battery 1) 12.63V Battery 2) 12.71V Terminals are tight. I am currently running a monitor, laptop and modem at 236v. If I put the TV and Soundbar on it goes to 239V.
  6. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Morning, System has been resting (unplug at mains and unit turn off) for 4hrs. Battery 1) 13.16v Battery 2) 13.18v I'm assuming the batteries are healthy and something else is causing the battery drain or could it still be an imbalanced battery?
  7. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Thank you. I'll give it a try
  8. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Hi, apologies how do I do that? I tested it during loadshedding. Disconnected the unit and used the multimeter.
  9. Devinc

    Mecer 2400VA Inverter (Community Support) - Part 2

    Hi, I have the mecer 2.4kva 1440w. My batteries were replaced 12 months ago under warranty, 100ah deep cycle batteries (through Mustek). 3 weeks ago the system started beeping and ran out of battery within 1hr of loadshedding. I only run a TV, soundbar and router on the system. The system...
Top
Sign up to the MyBroadband newsletter
X