2750W installed
Peak output in Winter around 2400W (Witbank)
Daily output 13.5-14.5kWh. Can probably get another 1.5kWh but from around 1pm I start struggling to use all the power generated
Hi,
Do you have the app?
Check your settings under the charging Tab. Under the "AC charge start SOC" try selecting to 99%. Also change start time to 00:00 and end to 23:59. Choose the AC charge option "according to battery SOC and time"
Also under the Application Setting Tab your AC first...
Hi,
I'm assuming you have things like geyser and stove running on non essential load (not connected to inverter). If this is the case something like the geyser is a 40% consumer of power and this alone may explain your 30% reduction.
Also,in order to maximize from your panels you need to try...
Hi,
Have you been able to get the settings done?
Not sure about setting on the Lcd but it's a fairly easy setup on the app.
1) set up the times you will like AC to power the house under application setting. Set to 00:00 if you don't want it to come in at all. So in your case you must ensure...