This is probably the most stupidest question on this thread, but is an "AC Transfer Switch" still necessary when wiring an Inverter between Grid and AC Loads?
:o :erm:
I ran a test with an Ellies efergy unit and e-link SW. The results indicated peaks/max power of up to 7kW at times.
So a single 5kVA Axpert is not going to be sufficient in this case, i.e. I would need two in parallel?
Cheers,
JP
I have tried to search the Forum, but it returns all sorts of results.
Is there any way for make up your own Grid-Limiter for Grid Tied Inverters?
It appears that not all of the Manufacturers have a built in functionality like this, so an external unit is required.
Thanks,
Question to all the "Axpert" experts.... ;)
Can you use this Inverter as a pure "grid-tie" unit, i.e. no battery bank?
Else, what other value for money grid-tie inverters are out there?
Thanks,
Relax... :erm:
My posts started out as questions and then I gave my opinion; that's it. :confused:
And no, I do not work for Victron or any other manufacturer for that matter.
But I am tired of "installers/companies" selling BS "off-grid" solutions consisting of one 4kW Inverter (Axpert or...
I do not have any test certificates, but neither does Axpert; why is that do you think?
The "more expensive" manufacturers all have test cases and certificates available.
Like I said in my post, it is "my 2c"; my opinion; use it, don't use it... :o
I was in contact with a Company that did performance tests on the 5kVA/4kW Axpert inverter.
Results were surprising, if not expected:
1. At around a 3800W load, the inverter started to struggle and quickly heated up.
2. At 40 deg C, the inverter's output fell to about 3000W
3. At 45 deg C it...
IMHO it's not ideal to have the inverter restart or even shut down.
More expensive inverters (and not by a country mile), will allow for grid pass thru of up to 56A in some cases, meaning that you will never be "disconnected" if the demand increases beyond the inverter's output.
One never knows...
Has anyone got temperature degrading information on the MKS Inverters?
As with any electronic device, heat plays a big role.
I have found this sort of spec with more expensive Inverters, which is quite useful, but nothing on the Axpert.
Also: My supplier informed me that the MKS 5kVA, although...