CoC requires isolator 1.5 from Geyser and Stove last time I checked.
Depends on the installation.
IE: 6.16.1.4 The disconnecting device shall be positioned a) within 1,5 m from the appliance, or b) in a distribution board (if the switch-disconnector is capable of being locked in the open position). Even where a disconnecting device is on the appliance, a separate disconnecting device shall be provided in the fixed installation to allow for the total removal of the appliance. NOTE A standard switch is not a switch-disconnector.
.16.3.1.2 A switch-disconnector for a cooking appliance(s) shall a) be in the same room as the appliance(s), b) be at a height above floor level of not less than 0,5 m and not more than 2,2 m, c) preferably not be above the cooking appliance(s), d) be within 3 m of the appliance(s), but within 0,5 m of the appliance(s) if the switch-disconnector's purpose is not clearly indicated, and e) not be fixed to the appliance.
Many ways to screw the system ,bend a bracket to cover your isolator so it can lock and voila ,isolator problem solved .
I can CoC virtually any install just by using the correct tools and understanding the regulations its the younguns that dont know the old regs ,going back to the factory act .