According to wiring code:
If buried less than 0.5 m below, it needs to be in a conduit, otherwise mechanically protected (paving or concrete slab), or protected by earth leakage with 30 mA or smaller rating.
If buried at least 0.5 m below, the backfill has to be clear of sharp objects and you need to place marker tape the full length of the cable at 0.3-0.4 m below the surface.
You are only allowed a 5% voltage drop, so on single phase (240 V) that will be 12 V. On a 16 mm² cable over 200m, that means a maximum current of 21.4 A (using 2.8 mV/A/m voltage drop).