I've got an existing 8kw - if I add ANOTHER 8kw unit then can I use a different battery brand (as it's a different inverter) or do I need the same?
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
From my limited knowledge, the short answer is no.I've got an existing 8kw - if I add ANOTHER 8kw unit then can I use a different battery brand (as it's a different inverter) or do I need the same?
They don't have to be the same exact firmware. When the hardware changes slight, so does the firmware version.If you add a second inverter if it isn't the same one as the old one that can properly parralel
(They have to be same model with same firmware to be able to parralel )
you have to seperate your load again to have 2 seperate critical load sections in the db and decide which loads goes on which inverter ie like you have it separated now, You have a critical loads circuit and a non critical loads, just 3 sections instead of 2 then
Yea if they are parralel then you don't have to seperate/divide the critical loadsThey don't have to be the same exact firmware. When the hardware changes slight, so does the firmware version.
But I think the rule of thumb is that if you have the latest firmware for each device at installation, then it will work.
On the main sunsynk thread it was covered a few months ago.
There's also no separating of critical loads. The 2 inverters connect to the same load and same battery bank.
The aux ports stop being of any use as far as I know, at least with generator input. I could be wrong with aux outputs, but gen input doesnt work. Check the wiring diagram in the sunsynk manual and you will see the load connections, grid connection, etc.