40 amps is not enough. You need to match to your mains circuit breaker as your full current runs through the switch.
Even if I am splitting the lights/plugs from the stove/geyser on the DB? Not interested in powering those from the 3 or 5 kVA inverter. My DB, wired in 1987, has 60A main, then stove/geyser and then a 30A earth leakage with the plugs and lights hanging off that. Will put the changeover between the EL and the main breaker for Eskom and feed the inverter into the other side of the changeover. This is still in the early-planning phase and my pet electrician hasn't been consulted as yet. Will appreciate input.