Screw on top is usually only for delay ,pressure is not adjustable ,these things dont work like a compressor air switch ,some are current sensing so ie a 350 watt pump will give you 3 to 5 bar etc .that unit won't have any complicated internals ,screw the head and pump off and take it back ,don't take it apart .edit ,that's a 750 watt pump ,so 7.5 bar is spot on,ps you don't need higher than 4 bar in a home but the way pumps are specced aren't at all logical ,also a lot of pumps wont turn on if your geyser is high up as the head will prevent startup if only hot water is drained .i am having trouble with my automatic pump flow control unit from mac afric.
How do i adjust the maximum presure or presure limit? It is curently running up to 7.5 bar and adjusting the screw at the top does not adjust the presure limit.View attachment 1763964View attachment 1763965
Per Soulie post, I have not discovered any change in pressure with these types of devices.i am having trouble with my automatic pump flow control unit from mac afric.
How do i adjust the maximum presure or presure limit? It is curently running up to 7.5 bar and adjusting the screw at the top does not adjust the presure limit.View attachment 1763964View attachment 1763965

Get a DAB mini easybox.
You can set the pressure margin, and it's quiet
PS ,I hope you set the flow switch back to where it was ,if not correct ,under high flow conditions ie tap fully open to run a bath ,it will turn off every 10 seconds if it can't maintain the preset flow rate.
Those are damn expensive.Get a DAB mini easybox.
You can set the pressure margin, and it's quiet
Yep, it's working as it should.That screw doesn't adjust the flow rate, it adjusts the pressure differential. In the case of these units, this basically translates only to the "turn on" pressure.
In more detail; when you open a tap, the pressure drops. When it hits the set point (usually the screw allows an adjustment from 1.5-3 bar) then it turns on.
When you turn the tap off, the pressure rises again. When it hits the "turn off" pressure (also controlled by the screw, since the screw adjusts the differential) it signals the pump to turn off.
BUT with these units there is a ~10 second delay before the pump actually turns off. This delay is what causes the pressure to rise even further up to the pump's maximum pressure.
They put that delay in there to prevent fast on/off cycling of the pump when the flow rate is low.
I know exactly how they work ,I install and service them. You have a lower limit which when at the lower position allows the pump to turn on ,the upper limit turns it off ,if at the lower limit and there isn't enough flow to lift the diaphragm it will cut the motor after 10 seconds .how many have you installed and serviced or is it just Google talking ,and that is why they are sold as flow switches and not pressure switches .That screw doesn't adjust the flow rate, it adjusts the pressure differential. In the case of these units, this basically translates only to the "turn on" pressure.
In more detail; when you open a tap, the pressure drops. When it hits the set point (usually the screw allows an adjustment from 1.5-3 bar) then it turns on.
When you turn the tap off, the pressure rises again. When it hits the "turn off" pressure (also controlled by the screw, since the screw adjusts the differential) it signals the pump to turn off.
BUT with these units there is a ~10 second delay before the pump actually turns off. This delay is what causes the pressure to rise even further up to the pump's maximum pressure.
They put that delay in there to prevent fast on/off cycling of the pump when the flow rate is low.
Why are you being so touchy?I know exactly how they work ,I install and service them. You have a lower limit which when at the lower position allows the pump to turn on ,the upper limit turns it off ,if at the lower limit and there isn't enough flow to lift the diaphragm it will cut the motor after 10 seconds .how many have you installed and serviced or is it just Google talking ,and that is why they are sold as flow switches and not pressure switches .
set the flow switch back to where it was ,if not correct ,under high flow conditions ie tap fully open to run a bath ,it will turn off every 10 seconds if it can't maintain the preset flow rate.
So is your wife...Those are damn expensive.
You either buy the dab or you buy the Mac and then the dabI'd imagine there is massive price difference between Mac Africa and DAB
You either buy the dab or you buy the Mac and then the dab
Have you have any experience with the shop or the product?Or just get a Switchmatic 2 and save 95% of your money.
Coelbo T-Kit Switchmatic 2 | DIY DIRECT SA
www.diydirectsa.co.za
Or a DPR and save 85%:
Coelbo, DPR 1″ Electronic Controller | DIY DIRECT SA
www.diydirectsa.co.za
Have you have any experience with the shop or the product?
Longevity?
At a R1000, its about double the price of the mac flow switch, but if it can set the pressure, it could be what OP needs.