Hi Roux, have you progressed with this project?
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
Not allways the case what i have found installing panels as i have cash meaning the voltage was at a stage very close to startup voltageBetter to run them in parallel if only 1 panel is enough to start the solar controller.
Iirc there is shading.Not allways the case what i have found installing panels as i have cash meaning the voltage was at a stage very close to startup voltage
Lifting the voltage by just one extra panel made a massive difference to the production
ie on the hot days the voltage vmp/voc drops and to stay in the mppt range panel has to produce power at a higher voltage sometimes dragging it into voc voltage where output be almost nothing
So you definitely don't want to be too close to startup voltage
Yea on 12/24v systems with a high cell count panel you won't bump into thisIirc the panels in question are 150W.
Sorry I edited my post. Have you read the thread?Yea on 12/24v systems with a high cell count panel you won't bump into this
But yea if you have lower cell count panels the same pitfall applies
You want your vmp to be at least 20-25% above startup voltage imo
Then Even WorseIirc there is shading.
Have you read the thread? Why are you responding to posts from 6 months ago?Then Even Worse
Then you want enough panels in series that after shading reduces them that you have a voltage still higher than bottom of mppt range
Not recently a while back and know that roux did up his panels count and changed inverter too if i remember correctly, different threadHave you read the thread?
so you remember it was a 500W panel on a 1000W inverter then so has more than enough startup voltage?Not recently a while back and know that roux did up his panels count and changed inverter too if i remember correctly, different thread
New post got me onto the thread again
Since i got my panels up , one panel at a time, the increase in production with each addition wasn't linear on the bottom of the voltage range , once a decent amount over mppt bottom then it was linear
and just thought to mention that just,just making it into mppt range isn't ideal
Yesso you remember it was a 500W panel on a 1000W inverter then so has more than enough startup voltage?
Please read the thread again as you are reading my parallel advice out of context or something.Yes
For a 12v/24v system it would take some effort/shading to get it wrong as most big panels exceed the startup voltage by a decent margin
The saga continued here.Hi Roux, have you progressed with this project?