Electrical Cable Installation in Ceiling Void

andre1809

Active Member
Joined
Aug 14, 2023
Messages
85
Reaction score
34
Am I allowed to run a single phase 16mm x 3-core unarmoured cable in my house'e ceiling void, between my main distribution board and a sub distribution board?

I am reluctant to use an armoured cable since it is so unyielding to work with in a confined space.
 
Last edited:
It needs to be double insulated and the breaker needs to be correct for the cable/distance but it doesnt have to be armoured.
 
It needs to be double insulated and the breaker needs to be correct for the cable/distance but it doesnt have to be armoured.
Cable will be a 16mm square 3-core of 26-28 meter length, running in a steel trunking in the ceiling void. Cable will be double insulated, with a 50 Amp breakers in both distribution boards. Main distribution board has an 80 Amp mains breaker. 16mm Square can handle up to 83 amps continuoustly.

Just needed affirmation thanks. :) :thumbsup:
 
  • Like
Reactions: B-1
Cable will be a 16mm square 3-core of 26-28 meter length, running in a steel trunking in the ceiling void. Cable will be double insulated, with a 50 Amp breakers in both distribution boards. Main distribution board has an 80 Amp mains breaker. 16mm Square can handle up to 83 amps continuoustly.

Just needed affirmation thanks. :) :thumbsup:

50a at 28m should be about 10mm^2 so your 16 will be good.
 
Cable will be a 16mm square 3-core of 26-28 meter length, running in a steel trunking in the ceiling void. Cable will be double insulated, with a 50 Amp breakers in both distribution boards. Main distribution board has an 80 Amp mains breaker. 16mm Square can handle up to 83 amps continuoustly.

Just needed affirmation thanks. :) :thumbsup:

16 mm cable in a wireway at 30deg c gives you a current of 63 amp max .
double insulated ? ,if youre talking of a standard unarmoured 3 core cable, thats pvc coated with a sheath thats not double insulated ,but in a roof space its not needed .
your correction factor can be as high as 0.80 with a max temp of 50 c,also make sure the cable isnt 3 phase cable on a single phase install ,its not compliant ,if not done correct youre throwing money away and wont be happy with the end result ,which could be a burnt cable or bad harmonics .
 
Last edited: