Electricity mains tripping when power returns after loadshedding

Ecco

Honorary Master
Joined
Jun 4, 2007
Messages
11,768
Reaction score
9,153
Hi good folk,

Please can you help regarding what to do to resolve issue of the mains tripping when loadshedding ends. We are travelling away for a week shortly and biggest concern is our chest freezer and food spoiling because the mains trips and electricity remains off for a whole week.

Trouble is this is not a regular occurrence, i.e. it does not happen every time loadshedding ends. Its very random but has been happening enough to warrant concern. Pattern wise i think its typically when loadshedding ends in the evening that i find this happens the most.

What are some of the things i can do to resolve this issue?

Thanks in advance.
 
Maybe a shot in the dark as to why it typically happens at night - we have 3 aircons and those are on at night? Could be a culprit? Dont think this solves the problem but maybe sheds light on the root cause?
 
I'd hazard a guess it's probably earth leakage having a fit from the sudden load. Are your aircons DB connected or plug connected?
 
It is only caused by an imbalance between outgoing and incoming current

1 - Make sure only plugs are connected
2 - Check anything outdoors for fidelity of plugs and connections
3 - Unplug everything not immediately required
4 - Check the plugs and sockets of fridge and freezer
5 - Check the connections to the fridge and freezer compressor
5 - Blow out the compressor motors

A megger will detect any compromised insulation. Replacing the e/l relay is useful, but not a fix
 
How many geysers, fridge/freezers, pumps do you have? And you said mains not earth leakage right? Im assuming a 63 amp breaker?
 
How many geysers, fridge/freezers, pumps do you have? And you said mains not earth leakage right?

I dont even know the difference between earth leakage vs mains. The two green switches are down, have to pull then full down and then up to get things going.

Have 1 fridge freezer combo, 1 chest freezer. Pumps? Pool pump - but its off at night. 2 Geysers.
 
I dont even know the difference between earth leakage vs mains. The two green switches are down, have to pull then full down and then up to get things going.

Have 1 fridge freezer combo, 1 chest freezer. Pumps? Pool pump - but its off at night. 2 Geysers.
Perhaps post a pic of the switch that trips. There's a significant difference between why a mains switch and earth leakage would trip.
 
I dont even know the difference between earth leakage vs mains. The two green switches are down, have to pull then full down and then up to get things going.

Have 1 fridge freezer combo, 1 chest freezer. Pumps? Pool pump - but its off at night. 2 Geysers.


If you are running all those on a 63 amp breaker/earth leakage its also too much.
As a rough guess the startup currents are:

2x Fridge/freezer @ 10amps each
3x Air con @ 10amps each
2x geyser @ 17amps each

That's possibly 84amps already depending on the type and size so definitely a problem if you are on a 63a breaker.


But get us a pic like requested above and we will have more info to go on.
 
Last edited:
Perhaps post a pic of the switch that trips. There's a significant difference between why a mains switch and earth leakage would trip.

Cool. At work now, will take a pic later
 
Pic as requested...it's the earth leakage that's tripping...those two green ones in the middleScreenshot_20221018_111058.jpg
 
I had a similar situation after we added solar to the house, turned out that the earth leakage breaker was defective. We replaced that, and all was good - not a single trip since then.

I'd start there?
I would say the EL or there are issues with the fridge/freezer when it starts up?
I have a unit that occasionally trips if we have lightning strikes near by!
 
Fridge freezer combo and chest freezer are relatively new - max 2 years old.
 
We had it also after our solar and 3 phase inverter system was installed. The main earth leakage feeding from Eskom into the Inverter would trip on the DB board sometimes when Eskom came back. I mentioned it to the installers and they did something on the inverter side and it stopped happeing. Not sure what it was.
 