I've recently installed (horizontal) a new 150l geyser (https://www.ariston.com/en-za/products/electric-water-heaters/electric-storage/axios-geyser) and replaced the 3kW element with a 2kW element. I want to heat the geyser primarily when I'm producing more solar than my house and batteries can accept.
I bought a Geyserwise TSE for temperature measurement - the plan is to replace the display unit with a Geyserwala Connect so I can get the reading via MQTT into HA/similar. But I'm having a problem with step 1 of the process... getting a temperature reading that I can trust. It seems to me that the reading from the thermistor is often less than the reading at the hot water outlet. I "understand" that the probe is near the cold water inlet of the geyser, and the potential issues around stratification, but I'm hoping you could explain the following behaviour that I'm seeing:
- As soon as I use hot water, the temperature reading drops to around 20 degrees C. I'm guessing this is because the probe is located near the cold water inlet.
- When the geyser is heating, the temperature rises fairly slowly. I have a CBI Astute in line with the geyser, so I'm able to use the temperature reading in conjunction with the power consumption reading and the specific heat equation to verify that the temperature reading is lower than expected
- When the Geyserwise turns off power (at the setpoint 55 degrees) the temperature continues to rise for 1.5 to 2 hours later. For example, on one day the element turned off at 14:55 (temperature was 55 degrees) but it continued rising until it read 65 at 17:25.
- All the above I can deal with and factor in when I get to my HA implementation. My major issue is that on more than one occasion in the last 2 weeks, with the temperature setpoint at 55 degrees C, my TP valve opened. This appears to confirm that the reading at the Geyserwise probe and the actual water temperature near the TP valve is very different.
Has anyone else experienced this? If I understand correctly, this means that the 90 degrees mechanical cutout is ineffective for my setup, because the TP valve is venting before the thermostat cuts out?
I've had two different installers come out to confirm that the probe is correctly inserted and pushed in all the way. I've even bought a new Geyserwise probe to replace the original (which was only 3 weeks old anyway...) just in case there was an issue, and it has vented at least once since the probe was replaced.
I'm at the point where I'm considering putting the original thermostat back in, so that it least power cuts out before the TP valve opens. And then look for another place to measure the temperature with the Geyserwise probe.
Has anyone experienced something similar? I'm wondering if it has something to do with my geyser construction (forgive my ignorance). Would you recommend putting the probe into the "renewable energy port" in this geyser, or is there a way to put it at the outlet?
Thanks!
I've recently installed (horizontal) a new 150l geyser (https://www.ariston.com/en-za/products/electric-water-heaters/electric-storage/axios-geyser) and replaced the 3kW element with a 2kW element. I want to heat the geyser primarily when I'm producing more solar than my house and batteries can accept.
I bought a Geyserwise TSE for temperature measurement - the plan is to replace the display unit with a Geyserwala Connect so I can get the reading via MQTT into HA/similar. But I'm having a problem with step 1 of the process... getting a temperature reading that I can trust. It seems to me that the reading from the thermistor is often less than the reading at the hot water outlet. I "understand" that the probe is near the cold water inlet of the geyser, and the potential issues around stratification, but I'm hoping you could explain the following behaviour that I'm seeing:
- As soon as I use hot water, the temperature reading drops to around 20 degrees C. I'm guessing this is because the probe is located near the cold water inlet.
- When the geyser is heating, the temperature rises fairly slowly. I have a CBI Astute in line with the geyser, so I'm able to use the temperature reading in conjunction with the power consumption reading and the specific heat equation to verify that the temperature reading is lower than expected
- When the Geyserwise turns off power (at the setpoint 55 degrees) the temperature continues to rise for 1.5 to 2 hours later. For example, on one day the element turned off at 14:55 (temperature was 55 degrees) but it continued rising until it read 65 at 17:25.
- All the above I can deal with and factor in when I get to my HA implementation. My major issue is that on more than one occasion in the last 2 weeks, with the temperature setpoint at 55 degrees C, my TP valve opened. This appears to confirm that the reading at the Geyserwise probe and the actual water temperature near the TP valve is very different.
Has anyone else experienced this? If I understand correctly, this means that the 90 degrees mechanical cutout is ineffective for my setup, because the TP valve is venting before the thermostat cuts out?
I've had two different installers come out to confirm that the probe is correctly inserted and pushed in all the way. I've even bought a new Geyserwise probe to replace the original (which was only 3 weeks old anyway...) just in case there was an issue, and it has vented at least once since the probe was replaced.
I'm at the point where I'm considering putting the original thermostat back in, so that it least power cuts out before the TP valve opens. And then look for another place to measure the temperature with the Geyserwise probe.
Has anyone experienced something similar? I'm wondering if it has something to do with my geyser construction (forgive my ignorance). Would you recommend putting the probe into the "renewable energy port" in this geyser, or is there a way to put it at the outlet?
Thanks!