c3n0byt3
Expert Member
Hi all, long post ahead...
I've been looking for a backup solution and think inverter+batteries are the best choice for me.
It's in home and will power a few appliances for ~4 hours.
It need not have a UPS feature and will be plugged into appliances when needed.
So on the inverter size needed I have this.
Considering inverter efficiency of say 80% then I have total size of ~640VA.
Yes I know some thumb sucks, but hopefully on the conservative side?
We have one of those Eskom smart meters and spot usage is always <300W with all above running (fridge too) + some lights (with geyser switched off). If the fridge is quiet it's around 100W.
On the battery side is where I'm having trouble. I have this so far.
* Other facs: Temp, age, DoD, wiring
I'm assuming 12v as this seems most popular.
Ultimately, I don't know what this all means in terms of actual available batteries.
If a battery is say 105ah then do I need like 4?
Can I balance cost of lithium batteries vs adding more non-lithium batteries and discharge >50%??
On set up, I'll probably place it behind our couches (closest to fridge) and run extensions from there.
Then on actual purchasing, stock seems to be a problem right now.
I'll need a pure sine wave inverter for the fridge right?
Then it needs to be >640VA? Does speccing higher help?
For 4 hours do I really need total 430A? The surge factor on the fridge is purely for that startup.
Am I missing some pieces wrt inverter+batteries? Looking at Geewiz makes it easier to add on trolley and batteries.
What else do I need?
I've been looking for a backup solution and think inverter+batteries are the best choice for me.
It's in home and will power a few appliances for ~4 hours.
It need not have a UPS feature and will be plugged into appliances when needed.
So on the inverter size needed I have this.
| Appliance | watts | surge fac | power fac | final watts | VA load |
| TV | 125 | 1 | 0.9 | 125 | 139 |
| Mibox | 10 | 1 | 0.9 | 10 | 11 |
| Fridge | 150 | 2 | 0.9 | 300 | 333 |
| ONT-Router | 25 | 1 | 0.9 | 25 | 28 |
| Total | 460 | 511 |
Yes I know some thumb sucks, but hopefully on the conservative side?
We have one of those Eskom smart meters and spot usage is always <300W with all above running (fridge too) + some lights (with geyser switched off). If the fridge is quiet it's around 100W.
On the battery side is where I'm having trouble. I have this so far.
| Run time (hrs) | Volts | DC A/h | Init DC A | Other facs* | Final DC A |
| 4 | 12 | 43 (Total VA / Volts) | 170 | 2.5 | ~426 |
I'm assuming 12v as this seems most popular.
Ultimately, I don't know what this all means in terms of actual available batteries.
If a battery is say 105ah then do I need like 4?
Can I balance cost of lithium batteries vs adding more non-lithium batteries and discharge >50%??
On set up, I'll probably place it behind our couches (closest to fridge) and run extensions from there.
Then on actual purchasing, stock seems to be a problem right now.
I'll need a pure sine wave inverter for the fridge right?
Then it needs to be >640VA? Does speccing higher help?
For 4 hours do I really need total 430A? The surge factor on the fridge is purely for that startup.
Am I missing some pieces wrt inverter+batteries? Looking at Geewiz makes it easier to add on trolley and batteries.
What else do I need?