Hope to get some clarity and help from the people who have a lot more insights than myself 
Setup is 3000W inverter, and has some older panels, apparently 4.45kWp
Bought a house, which has had an older solar installation - probably installed about 8y ago and has been functioning with no issues. Returned home 2Jan 2026 with burnt smell and inverter no longer functioning - decided to send to insurance. They came back and said there are too many panels for the inverter, and this is a design defect.
I did calc:
Isc PV (Maximum Input Current): 18A
Nominal Operating Voltage: 360 Vdc
Mathematically, my installed 4.45 kW array, operating at the nominal 360V, generates approximately 12.3 Amps of current (4450W / 360V = 12.36A)
This is within the manufacturer’s certified limit of 18 Amps?
Is my assumption wrong with the above?
Insurer:
4.5 Technical Assessment Summary
A 3 kVA inverter is fundamentally unsuitable for supporting a 4.45 kWp PV array, especially when coupled
with the existing connected electrical load. The system configuration is technically incorrect, non-compliant
with industry best practices/ and violates standard engineering principles for solar PV installations.
The observed inverter failure is a direct consequence of this incorrect system sizing and subsequent chronic
overloading, rather than normal wear and tear or manufacturing defect. The system was designed and
installed in a manner that guaranteed premature failure of the inverter.
This capacity mismatch dictates that the inverter was operating continuously beyond its designed limits for
power conversion and thermal dissipation. Such sustained overloading induces excessive thermal stress on
the inverter's internal components. Furthermore, the inverter is not adequately sized to handle the electrical
load being drawn through the system, exacerbating the overstress condition.
Inverter spec:
From the Inverter: Model No. : EPHS-ICON-1P-01A Serial No. : 96131604100418
Setup is 3000W inverter, and has some older panels, apparently 4.45kWp
Bought a house, which has had an older solar installation - probably installed about 8y ago and has been functioning with no issues. Returned home 2Jan 2026 with burnt smell and inverter no longer functioning - decided to send to insurance. They came back and said there are too many panels for the inverter, and this is a design defect.
I did calc:
Isc PV (Maximum Input Current): 18A
Nominal Operating Voltage: 360 Vdc
Mathematically, my installed 4.45 kW array, operating at the nominal 360V, generates approximately 12.3 Amps of current (4450W / 360V = 12.36A)
This is within the manufacturer’s certified limit of 18 Amps?
Is my assumption wrong with the above?
Insurer:
4.5 Technical Assessment Summary
A 3 kVA inverter is fundamentally unsuitable for supporting a 4.45 kWp PV array, especially when coupled
with the existing connected electrical load. The system configuration is technically incorrect, non-compliant
with industry best practices/ and violates standard engineering principles for solar PV installations.
The observed inverter failure is a direct consequence of this incorrect system sizing and subsequent chronic
overloading, rather than normal wear and tear or manufacturing defect. The system was designed and
installed in a manner that guaranteed premature failure of the inverter.
This capacity mismatch dictates that the inverter was operating continuously beyond its designed limits for
power conversion and thermal dissipation. Such sustained overloading induces excessive thermal stress on
the inverter's internal components. Furthermore, the inverter is not adequately sized to handle the electrical
load being drawn through the system, exacerbating the overstress condition.
Inverter spec:
From the Inverter: Model No. : EPHS-ICON-1P-01A Serial No. : 96131604100418
Section | Specification | Value |
PV INPUT | Nominal operating voltage | 360Vdc |
Vmax PV | 500Vdc | |
Isc PV | 18A | |
MPPT voltage range | 250 - 450Vdc | |
GRID/AC OUTPUT | Nominal operating voltage | 230 Vac |
Maximum output current | 17A | |
Nominal operating frequency | 50Hz | |
Maximum power | 3000W | |
Power factor range | 0.9 lead-0.9lag | |
AC INPUT | Nominal operating voltage | 230 Vac |
Maximum input current | 30A | |
Nominal operating frequency | 50Hz | |
BATTERY | Battery voltage range | 42-56Vdc |
Minimum capacity | 125Ah | |
Maximum battery current | 82A |