The calculation assumes a battery with 24V and 100Ah capacity... So that is 2 x 12V 100Ah batteries in series.
A quick way to check this is to calculate the number of kWh that you need (just kW x hours) compared to the kWh of your battery.
So if you need 500W for 3 hours, you need 1.5 kWh.
A 12V 100Ah battery gives you 1.2kWh. But if you limit to 50% depth of discharge you only get half that - 600Wh.
I just put in some dummy data as an example, you can update the various variables and the time will auto update.
Is the formula for block F2 always ½ of that of block E2 ? ... and also, is that half(50%) the Ah usage ??