I know that, but the spec sheet conveniently forgets to mention voltage. Anyway the voltage will drop as the batteries are depleted, so 8800mAh can't simply be multiplied by 3.7V.
Is there a specific reason you want to know the amps
You can calc what the bottom and top will be by the discharge graph
ie cell will go as low as 3v and as high as 4.2v
so you can say if you pull 1c
ie 32w then 32/3=10.66A
And 32/4.2= 7.619A
at battery level naturally
your amps will be constant on the voltage of the device as the converter steps it up or down to meet that
ie if you pull the 32w for an hour on 12v the amps on the wire that supply it will be 2.66a approx throughout that hour
8.8a is the avg over that hour, though not the avg of the extreme top and bottom
ie if you can pull 32.56w for an hour they convert that to give us the AH rating by dividing it by the nominal voltage as that what most people use to calc ****
So if you discharge at 1c ie use the capcity in one hour if it is rated to do so
You would start at 7.619a and end at 10.66a
I try and switch all my calcs to watt since that is the same irrespective of voltage
And what you will need when looking for a battery as most are rated in Wh/KWh
if i get a battery that is ah rated i convertd it to watts