Here's the current for my one north facing string yesterday. The panels are rated for 18.4A (Isc). As you can see, they only get close to that for a small portion of the day. If, for example, you paralleled your strings to 20A any potential losses really would be minimal.
You don't need to hit max amps
On an mppt for it the give you all the panels can produce
Amps and volts are just two variable that determines your watts
You want to stay away from inverter max volts to prevent frying the controller
And stay away from the max amps to not have losses
The volts/amps rise as the sun angle rises having higher amps panel doesn't mean you get more out of panels
(and naturally the inverter can choose the volts at which it chooses to extract those amps)
In fact if going too high in the amps you narrow the band in which the inverter can choose from as you need to do lower volts to fit in the max watts
If any shading that band narrows further
The wider the band the better shade can be dealt with before dropping out of mppt range, dropping out of mppt range is way way worse than some shade
Many confuse dropping out of mppt range as shaded panels killing the array amps
This is worse on low voltage mppt , by going higher amps you are turning a high voltage into a low voltage mppt by choice sacrificing all the advantages brought by high voltage mppt because people don't understand this