Expert Member
Not too sure, but it does have an Earth leakage button underneath? Please see pic.
It’s an old house with one plug point per room. Study has two computers plugged in and various laptop chargers. Bedroom has 55” TV and two consoles. Lounge a 65” and 32” TV with one console.
Could these be leading to overloading due to one plug point per room? Even though they’re off when power comes back on?
Looks like there are five plug breakers. I think I’ve tried switching them off and then on again and they don’t cause the main breaker to trip.
Seems to only happen most of the time after load-shedding ends and power comes back on. Or most of the time when plugging in computers and laptop chargers... It’s temperamental in sometimes it doesn’t trip.
What’s the power isolator? The main breaker?
Please see pic.
Looking at your board it seems only your plugs and lights have earth leakage protection. Your geyser, stove and oven is not protected. You don't seem to have too many devices connected to cause more than 30ma leakage which is standard for a domestic unit. The only way to know for sure is to measure the amount of leakage occurring which you need expensive test equipment for. I would recommend you do a board change and add another earth leakage unit for the unprotected devices. If you had alterations done to the original electrics it might be that you have a neutral shared with an unprotected device but this would cause a lot more tripping. I would replace the earth leakage first and see what happens.