Ah ok, 10 panels - I misread there. So the input side of the inverter (very nice inverter, with built in regulator/charger, BTW) is 48V, meaning you'd need some combination of series/parallel with your panels to get a 48V input to the regulator. So 15m at 48V and a 2400W array equals around 50 amps of current in your wiring. You'd need 13mm2 wiring.
http://www.freesunpower.com/wire_calc.php
http://www.technick.net/public/code/cp_dpage.php?aiocp_dp=guide_awg_to_metric
A basic rule of thumb you can use for DC cabling up to 20m lengths is:
Maximum 4A per 1mm² cable.
I would wire each series string seperately and bring them all together in a combiner box. Before combining each of the strings in parallel put a fuse on each of them so that you can isolate each of the strings seperately for maintenance.
This has a number of advantages:
1. You can do maintenace on each series string seperately and still use the other strings for generating electricity.
2. You only need a very short piece of (13mm2) expensive cabling from the combiner box to the charge controller.
3. Depending on the current generated by each series string, you should only need 4mm2 to 6mm2 cable.
There is however one disadvatage to this setup. You need more cable to connect all your series string to a combiner box.