Synsync Parity Inverter Settings

JV_011_

Senior Member
Joined
Sep 13, 2012
Messages
653
Reaction score
33
Location
Centurion
Hi guys, so i need help.

I have just installed a parity inverter and it comes with a coil that feeds power back to the grid( plus that are not passing through the inverter). This is causing me headache. If i switch on a kettle thats on the grid, Its draining my battery power instead of using the power from the grid.

How do i make sure that ONLY excess power from the solar can go through the coil?.

I need help with the settings.

On a different note: The solarman app, how do i get information about how much data is comming from the battery vs panels vs the grid ?
 
Go to www.powerforum.co.za, lots of help there..
But essentially what you are asking can be found in the "system mode" menu...this is where you will find the required settings..
 
Hi guys, so i need help.

I have just installed a parity inverter and it comes with a coil that feeds power back to the grid( plus that are not passing through the inverter). This is causing me headache. If i switch on a kettle thats on the grid, Its draining my battery power instead of using the power from the grid.

How do i make sure that ONLY excess power from the solar can go through the coil?.

I need help with the settings.

On a different note: The solarman app, how do i get information about how much data is comming from the battery vs panels vs the grid ?
Post a pic of your settings screens.

I have the 8kw sunsynk inverter.

Also what batteries and solar panels do you have?
 
1ce60e82b8dd127c2c2185f835cebd2b.jpg


I have 10x 455W JA panels
2x 5.5kw hubble Lithium batteries
 
So here is my latest try.
1614770802075.png


and this gives me this
1614770843546.png


Ideally what i would like to do is
1, charge my battery till max.
2, if there is solar, provide power to the load and or charge battery till max. excess power goes back to the grid.
3, if no solar, use battery but dont send power to the grid.
3.1, kettles needs power, get it from the grid and not the battery.

this should happen till my battery is 35% at night then from there use the grid.

I have 9 X Canadian panels - 340W
5KW inverter
4 X 200A gel batteries that i am replacing with a 1 X 100A lithium 5.6KW battery soon.
 
I saw when i switched on the kettle these were my readings.
1614771136660.png
 
Last edited:
So here is my latest try.
View attachment 1029930


and this gives me this
View attachment 1029932


Ideally what i would like to do is
1, charge my battery till max.
2, if there is solar, provide power to the load and or charge battery till max. excess power goes back to the grid.
3, if no solar, use battery but dont send power to the grid.
3.1, kettles needs power, get it from the grid and not the battery.

this should happen till my battery is 35% at night then from there use the grid.

I have 9 X Canadian panels - 340W
5KW inverter
4 X 200A gel batteries that i am replacing with a 1 X 100A lithium 5.6KW battery soon.
Put a tick in limit to load.
 