B-1
- Apr 17, 2020
Earlier this month, we had the good fortune of our substation catching fire. While 12 days to repair was reasonable, and my solar setup kept me going on the sunny days, I fell well short on the cloudy ones.
So the choice was either to buy 2–4 more batteries or get a generator. I went the generator route and bought a 5kW Gentech Pro inverter. I've been watching videos and playing with the settings to figure out the correct way to install it.
I think I have things mapped out, but the information out there (due to different install options) varies wildly, so I'd appreciate a double-check.
My generator is unbonded, and the Aux port on the Sunsynk inverter only runs in islanding mode, according to the videos I've seen. My install includes a relay to bond earth/neutral in islanding mode, which makes sense from a compliance point of view, as you're only supposed to have a single E/N bond.(If your generator is bonded dont do what I have done))
For the wiring, I connected the generator's Live and Neutral to the GEN/AUX port on the inverter, and the Earth to the earth point inside the inverter.
After wiring everything up, I set the Aux Load settings to "Gen Input", restricted it to 3000W, and set the "GEN Load ON Batt" to 80%.
I then set the "Batt Charge" settings as below. The amps indicate the generator amps on the left and the grid amps on the right. This is the battery current, so my 14A is very conservative, and I'll increase that for the next tests (14A × 50V = 700W). I selected the "Gen Force" checkbox so that it ignores my settings in the "System Mode" screen. (This is because I manually connect and start the generator as needed, so the "System Mode" screen isn't relevant to my use case.)
I ran a quick test and everything seems to be working as expected.
So that’s a quick run-through of what I’ve done. I’d appreciate any comments on my setup in case I’ve made any mistakes.