Please explain how you get 1280Wh with a 24V (under 400W voltage drop load) inverter shut down voltage.
ja id like to know
The problem is the supplier saying it has 1280Wh of capacity (technically true) but doesn't factor in the forced 24V cut off (20% SOC) but wait its worse because that 24V is under 400W load (voltage drop) so its closer to 25% soc, so 1280 x 0.75 = 960Wh.
960Wh/425W = 2.25 hours, which is 2h15 which is exactly on the nose how long the test lasted.
The 100W load will last even longer with the lower voltage drop allowing it to get closer to 20% soc.
So, there is no problem.
k but lets say its 960w / 100w / discharge loss its about 7h 40m (approx)
960 /425w / discharge loss = about 1 hour 50m approx
you working it out without any discharging loss so it is inaccurate.
see below
lets do it like this forget about the voltage etc its going to drive you and readers nuts.
battery is 1280wh which is a 50ah at 25.6v (25.6x50= 1280Wh)
Remember there is about 25% discharging loss when discharging power this is not a navasolar thing its all of them my Delta 2 does the same disperses in heat etc so energy loss from heat and i donno how else to explain it just does that.
The 1280wh SOC 80% so yes technically speaking don't drop below 20% threshold which will cause the BMS to go HEY controller this battery is below required and controller goes HEY DISPLAY scream the alarm battery too low
Considering these inverters were for AGM etc it relies on voltage from the battery but lithium is controlled by the BMS.
BMS no like BMS no give. BMS happy BMS gives. happy BMS happy power.
also for anyone reading these
BP18-1012 (1kva) is 960Wh
Ti-1512 (1.5kva) is 1280Wh
BP18-3024 (3kva) 2560Wh
Ti-3024 (3kva) 2560Wh
Ti-3052 (3kva) is 5120Wh
Use the simple maths when calculating run times Wh divided by watts amount divided by discharge amount and IF its gel or led acid divide by 2 since Gel/Lead-acid should not go below 40-50% battery Capacity due to their lower voltages to operate) otherwise you going to kill the gel/lead-acid battery and close to impossible to recharge them.
So If anyone is reading this and has lets say a RCT MP-T1000 which has a 12v 100ah gel battery if you change it to a lithium battery with a built in BMS it will last longer on the run time not necessarily double but close to it.
12x100ah (technically 12.8 x100 = 1280) if using lithium instead of 12x100 = 1200wh divided by SOC = 600Wh unusable (APPROX)
Remember NOTHING electrical is a stable amount of constant power unless controlled which no appliance does.
Computer can be 65w but fluctuates 55-95w depending what it is doing (gaming is a lot higher up to if not 650W+)
there is also more to it technically but in lament terms basically this. a Fridge states 100w just remember cold starts can be 6x if not higher on cold starts, while a TV is a LOT less considering the fridge has a motor (even if its digital)
Lithium designed inverters like the Mecer 2kva (the oval shapped one ish) can DO down to close to 0% not exactly wise to do but it can do it. Ecoflow Power station can go to 0% as well technicians will state dont do it but i know it can (dont do it unles it happens but battery management can stop it to keep the battery healthy) also the best way to re-sync those batteries anyway.