Yup so if this can happen to your geyserwise...imagine a Pow R2 LOLPeople are always in a panic about the Sonoff POW2 or TH16 not being up to the job of running a geyser.
Well today my Geyserwise...literally made for this job **** the bed when the relay popped and melted half the wiring along with it.
![]()
Now what are the chances of finding a hf2160-1a-12de somewhere local to replace this one? Or will I need to spend stupid money and replace the entire power supply?
If I had a spare TH16 and waterproof thermometer at hand I would have installed it already and thrown the entire thing out, but that’s probably as hard to find this weekend as said replay and power supply.
For now I’ve bypassed the whole thing but I suspect there is no other thermostat or overload in the geyser itself as this replaced it all, so now I’m just running it for 30min at a time and making a guess at the temperature.
My one geyser surprised me, has a 4kW element in which runs at 17amps, so there is no chance that would've worked on a Pow R2 anyways.
But yeah, bad time of the year for this to happen.
Btw, you only need to run the geyser for 60min a day in the current season. I noticed mine stays nice and hot throughout the night and day running only 1 hour a day. I then run it 5 hours 1 day a week to keep the legionnaires at bay.