Inverter connections

wingnut771

Honorary Master
Joined
Feb 15, 2011
Messages
28,144
Guys, it's not that hard. Plugs have a limit, for instance, our SA plugs are limited to 16 amps at 230vac. OPs inverter has a plug design limited to 1.5kW, let's call it 6 amps. The inverter is 6kW (4 plugs times 1.5kw) with a 10kW peak.

But yes OP, if you have a 2.5kW load you can wire 2 plugs in parallel to power your load. Just do a good and safe job.
Never heard of 6A plugs so I find it quite random to put that limit on the outlets.

Thank you for confirming the possibility of parallel connections. Can you parallel all 4?
 

deesef

Expert Member
Joined
Mar 3, 2017
Messages
2,627
Most 5 to 7kva generators have 2 sockets that are paralleled to the db. There is a Ryobi 10kva that has 4 sockets. I would assume that they would also be paralleled, if wired to the db. The only other way to connect such a big load would be to have heavy-duty cables via suitable connectors, as done with most brand-name inverters.
 

voxisslowasballs

Active Member
Joined
Jan 21, 2017
Messages
68
Never heard of 6A plugs so I find it quite random to put that limit on the outlets.

Thank you for confirming the possibility of parallel connections. Can you parallel all 4?

Not too familiar with foreign plugs, may be one of those. 6A is quite low though, I suspect it may be due to the wiring or PCB tracks going to the plugs IE using thin wires or tracks to save a few cents. So a capable plug, but too thin a wire going to it.

Anyway, yes, you can wire all 4 in parallel.
 

Neuk_

Executive Member
Joined
Jan 23, 2018
Messages
7,995
Never heard of 6A plugs so I find it quite random to put that limit on the outlets.

Thank you for confirming the possibility of parallel connections. Can you parallel all 4?

Would that not be a quadrallel then? Trademark pending of course, along with the rights to the GoPro footage.
 

Neuk_

Executive Member
Joined
Jan 23, 2018
Messages
7,995
Guys, it's not that hard. Plugs have a limit, for instance, our SA plugs are limited to 16 amps at 230vac. OPs inverter has a plug design limited to 1.5kW, let's call it 6 amps. The inverter is 6kW (4 plugs times 1.5kw) with a 10kW peak.

But yes OP, if you have a 2.5kW load you can wire 2 plugs in parallel to power your load. Just do a good and safe job.

For appliances that require 2.5kW, a good and safe job would not include an inverter like this.
 