Issue with LED lights when Load Shed kicks in

Igor III

Well-Known Member
Joined
Oct 5, 2015
Messages
222
Reaction score
12
I am running a solar system with Sunsynk Inverter and Hubble AM2 batteries. I have three rooms in the house that uses a 24 watt LED light (Eagle Lighting Ceiling Light) as per this link.

In essence, my solar system is set up to be the primary source and when required, the system will use Eskom to charge the batteries when at 25% or below. What I have noticed is that when we have load shedding (disconnected from the grid), these lights begin to "glow" (emitting low light), even though the light switch is in the off position. This is rather annoying for the late night load shedding schedules.

I am not sure if this is caused by the three step dimming feature of these units (I run them off a regular on/off light switch and do not use the dimmable feature), as all my other LED lights in the house do not exhibit this problem.

Is there a way that I can eliminate these lights from emitting low level illumination during load shedding, or would I need to replace these units (especially the ones installed in the bedrooms)?
 
We had the same problem with our Victron inverter until we discovered a fault in the underground cable to the cottage. This was causing a voltage difference between ground and neutral.
 
Sounds like the earth neutral bond isn’t working properly or wasn’t done at all, bleeding power into your system and it shows up on these lights because their requirements are so low.

The problem isn’t the lights, something is wrong with your system.

Get the installer to come fix it.
 
Thanks for the replies, much appreciated - I have notified my installer
 
Installer eventually checked the system and found that he forgot to install a neutral wire on the DB board between the municipal bank and the solar bank of isolators

All is working normally now

Thanks agaun for the inputs
 