Just recalculate as above using 240 V. The max current you can draw is determined by the rating of the CBs, which is 20A.That’s if the voltage is 220.
Mine is sometimes almost 240.![]()
But technically, if a wall socket is rated max for 15amps @ 220v (3300 watt), will it be unsafe to draw 15 amps @ 240v (3600 watt)?Just recalculate as above using 240 V. The max current you can draw is determined by the rating of the CBs, which is 20A.
Yes, it is 16A. And that is determined by the maximum rating of CBs, which are specified to be16A + 25% overload = 20A.But technically, if a wall socket is rated max for 15amps @ 220v (3300 watt), will it be unsafe to draw 15 amps @ 240v (3600 watt)?
I assume the socket equipment actually have a safety factor in it to actual function with higher loads than what is stated.
Edit, when did it change to 15 amps? Bought new wall plug replacements the other day, still states 16 amps max on it.
Just remember this is for the entire socket range.
Not 16 amps each
As the entire socket will be sharing 1 common set of wires going back to the ditribution wall
You cannot go 3000 watts on both sockets at the same time
View attachment 1207948
I just checked my flat and I have 7 wall plugs in total going to 3 x 20amp breakersWell beyond that, given how most houses are wired, its 3000watts across multiple plug points as well. You can just hope the DB board is labelled correctly, and that plug point isn't magically on a light circuit![]()
I just checked my flat and I have 7 wall plugs in total going to 3 x 20amp breakers
So if I ran 3500 Watts x 2 on each wall plug (they're double plugs as per previous pic) that equals 49000 Watts / 240volts = 204 amps
Either my maths sux right now after a few beers or I must never load my plugs with that many heaters
I have just had a CoC done. My home has 2.5 mm sq wiring and 30 A breakers with no more than 4 sockets per breaker.I just checked my flat and I have 7 wall plugs in total going to 3 x 20amp breakers
So if I ran 3500 Watts x 2 on each wall plug (they're double plugs as per previous pic) that equals 49000 Watts / 240volts = 204 amps
Either my maths sux right now after a few beers or I must never load my plugs with that many heaters
Are you selling? Where to?I have just had a CoC done. My home has 2.5 mm sq wiring and 30 A breakers with no more than 4 sockets per breaker.
This new crap using 1.5 mm sq wiring and 20A breakers is just a BS shortcut!
The electrician buggered around and scratched and finally found ONE socket that he says I have to change because it is tripping the EL at 30mA instead of 20 mA.
He wet himself because he found a circuit I use for the fridges and freezers NOT on EL. In fact, if my wife had kept her mouth shut he would not have found that circuit.
That is all he found. You should have seen the long face because both so-called problems were solved by me while he waited. A loose earth connection and I simply disconnected the other circuit. The new owner can do whatever he likes.
Not bad for a house that has not seen the likes of an electrician in 40 years.
I have just had a CoC done. My home has 2.5 mm sq wiring and 30 A breakers with no more than 4 sockets per breaker.
This new crap using 1.5 mm sq wiring and 20A breakers is just a BS shortcut!
The electrician buggered around and scratched and finally found ONE socket that he says I have to change because it is tripping the EL at 30mA instead of 20 mA.
He wet himself because he found a circuit I use for the fridges and freezers NOT on EL. In fact, if my wife had kept her mouth shut he would not have found that circuit.
That is all he found. You should have seen the long face because both so-called problems were solved by me while he waited. A loose earth connection and I simply disconnected the other circuit. The new owner can do whatever he likes.
Not bad for a house that has not seen the likes of an electrician in 40 years.
All plugs in residential install must be earthed on the earth leakage.Plugs supplying fridges , alarms systems , IT equipment doesn't not have to be on an EL.
Agree 100%All plugs in residential install must be earthed on the earth leakage.
Fridges are actually very critical to be on Earth leakage because what if the body becomes live due to a bad defrost heater or something else?
Exactly! The circuit was/is dedicated to fridges and freezers with specialised plugs and coloured covers.SANS10142-1
View attachment 1208234
Although best practice to have all your socket outlets connected to an EL, in terms of issuing a compliance certificate as in Geoff case you need to be careful when you use words like shall and must .