USE setting
Thank you, will give these settings a go. Can already see the battery voltage is now correct at 55.2.USE setting
06 = 55.2V
07 = 55.2V
08 = 46V
Not sure about 09 and 10
But what did you do just so that it's on record for anyone who cones across the issue in future?So far so good @wingnut771 thanks for your help friend appreciates it a lot.
The use setting uses setting 06, 07 and 08 in the manual.But what did you do just so that it's on record for anyone who cones across the issue in future?
Yes, 42 is too low, even 48V is still bad for AGM, 50V is much better. You can always change it if you need more from your batteries on that rare occasion.Hi Guys
So Finally got Solar panels just check there is no way to blend Solar and utility?
I have set it as follows , but just need to check is this the best for AGM Batteries till i can get a decent set of Lithium's hence not wanting to use batteries to power and save that for load shedding at night
been running on Solar/ batteries since 8am this morning it seems to be OK
Total wattage on the PV is only max 990W so I don't have the whole house running but seems to cater for what I am running.
So far its ok just early morning and evening when it goes a bit crazy swapping between Utility and PV
So lights flicker and other UPS picks this change over up and beeps (ill leave it can pretend we haunted)
Mecer 5kva SOL-I-AX-5P64
this is my settings anything I can change?
Program
01 SOL
02 20
03 UPS
04 SDS
05 AGM
06 LFE
07 LFD
09 50HZ
11 S20A
12 53 - I set this to 53 so it will hardly use the batteries - not sure if 54 is better to preserve them more
13 -Ful
16 SNU - Prefer this as solar wont charge fast enough so mix
18 bon
19 Feb
20 LON
22 AOF - Had to tur it off as it goes crazy in the morning and evening when PV is going off or coming on
23 BYD
25 FDS
26 56.4
27 54
28 Pal - I Didn't set this so not sure why its on PAL only inverter must i change to single or no difference
29 42V - Should I set this to like 48V to prevent the batteries being fully drained?
30 One
31 SBE
32 Aue
33 Eds
34 58.4
35 60
36 120
37 30d
38 dl5
39 ads