/facepalm
There is seriously flawed logic exhibited by some people here, please don't ever take up a career in designing critical power systems.
Really? care to point out the flaws in my logic? I'm sure there are many, hence why I can't put a finger on it
Most generators are self-contained units - so a fire in one of them won't threaten the rest of the building.
The one which I was working with many moons ago, was such an unit - separate from the main building itself.
But a proper DC will have redundant systems separately (separate buildings, separate from the main DC itself), or am I missing something here?![]()
It's a regulatory requirement to shut off generated power in a fire event apparently.
Really? care to point out the flaws in my logic? I'm sure there are many, hence why I can't put a finger on it
For example, why house all the gennies in the same building, same goes for ups etc. Everything should be contained separately in all stages of the power feed all the way from fuel tanks (contamination etc) to DB's with different cable routes etc. Split everything and keep it all separate with the option to cross connect as well..
Thanks for thatI don't work at Gallo Manor so I don't know the finer details but this is what happened yesterday.
Firstly...
MTN Business <--- (Huge gap) ---> MTN SP
They may share a name but they are two different companies.
The Eskom power went down at the Gallo Manor hosting facility and when the first generator kicked in a oil line running to the generator broke. The line started spewing oil over the exhaust which created a crapload of smoke and set off the fire alarms. That also caused the first generator to "explode". The fire alarms are set that if they detect a fire it shuts down everything including the automatic failover and that prevented the backup generator from kicking in.
Both the backup generators have weekly, monthly and quarterly maintenance schedules that are done and checked. There simply was no way that anybody could have forseen this happening.
*disclaimer*
This is a unofficial recount of what happened. A official explanation should follow some time today.
In this case, double facepalm.
some thoughts on reading this thread...
- MTNB HAS redundant systems, this was a MECHANICAL failure that could not be predicted.