I need some tech info on batteries. After using my UPS for over 3 years I decided to replace them with 2 x Koyosonic 12V 7Ah units. As the UPS works on 24V the 2 are charged and discharged in series.
What a big mistake to not look at hellopeter before buying. During the loadshedding of the end of May I found the one battery would go flat before the oher one. I did a 16 hour charge of both in the UPS and disharged them as per the spec sheet at a current of 1.8 amp. They had to be able to deliver 1.8A for 3 hours down to a voltage of 10.8V I would not have discharged them so low but that is the highest voltage for which specs are provided.
With the one battery much lower than the other one I contacted Sinetech 7 days after I bought them.
This is the response from Herbert Teubner the general manager from Sinetech
You have not tested the batteries correctly. Firstly, when you buy the batteries, new batteries never have 100% capacity immediately. You would have to first do 5 – 10 cycles to reach 100% capacity. In addition, the batteries have to be charged according to a proper charge cycle. UPS system do not normally have very sophisticated chargers, they are normally only float chargers. This will never bring the batteries up to 100% capacity. You never test batteries in series. You should test the batteries individually. So therefore your report does not make sense and is invalid.
When I requested them to charge the battery correct and prove the 3hrs load test @ 1.8A they ignored my e-mails.
The battery not close to spec it took only 2h 15min to reach 10.8V. The spec gave a time of 3 hrs and my test the temp was 4 degrees lower than their spec temp. After a few more discharges to bring it to 10 this battery only gave a time of 54 min. This is after 10 days since I bought them. Also it would not charge to a voltage higher than 12.7V
Can I please get some comments on what to do as Sinetech would not accept the battery is faulty. Also if some replies could be had from people in the know about the method of testing such batteries.
What a big mistake to not look at hellopeter before buying. During the loadshedding of the end of May I found the one battery would go flat before the oher one. I did a 16 hour charge of both in the UPS and disharged them as per the spec sheet at a current of 1.8 amp. They had to be able to deliver 1.8A for 3 hours down to a voltage of 10.8V I would not have discharged them so low but that is the highest voltage for which specs are provided.
With the one battery much lower than the other one I contacted Sinetech 7 days after I bought them.
This is the response from Herbert Teubner the general manager from Sinetech
You have not tested the batteries correctly. Firstly, when you buy the batteries, new batteries never have 100% capacity immediately. You would have to first do 5 – 10 cycles to reach 100% capacity. In addition, the batteries have to be charged according to a proper charge cycle. UPS system do not normally have very sophisticated chargers, they are normally only float chargers. This will never bring the batteries up to 100% capacity. You never test batteries in series. You should test the batteries individually. So therefore your report does not make sense and is invalid.
When I requested them to charge the battery correct and prove the 3hrs load test @ 1.8A they ignored my e-mails.
The battery not close to spec it took only 2h 15min to reach 10.8V. The spec gave a time of 3 hrs and my test the temp was 4 degrees lower than their spec temp. After a few more discharges to bring it to 10 this battery only gave a time of 54 min. This is after 10 days since I bought them. Also it would not charge to a voltage higher than 12.7V
Can I please get some comments on what to do as Sinetech would not accept the battery is faulty. Also if some replies could be had from people in the know about the method of testing such batteries.