So I'm probably going to go with the system from The Power Store as mentioned earlier.
I will need an electrician in the Somerset west area.
Just few questions.
Can this simply be hooked up into my DB without changing any of my existing plugs and light circuit breakers?
How will the system switch over when there is a power failure? Is it automatic? Will there be a delay from the time that Eskom goes down to when the back up system kicks in?
Can I set where electricity should be coming from?
Basically in the day the panels should should first supply the current electrical needs, excess capacity should then go to charge the batteries and any surplus after that should back feed into the grid. As it gets darker, electricity supply should then move over to Eskom. The only time battery power should be used is if the panels are not producing sufficient current AND Eskom is down.
My pool and pond pumps are already on a separate circuit breaker so will isolate this so that if Eskom goes out my panels and batteries are not used to run these.
I have a heat pump for my geyser so can run this from the inverter. Cooking with a gas oven and hob already so no need to do anything there. The only other items that draws huge amounts of current would be my washing machine, dishwasher and microwave. Will be replacing my current cfl lights with LED lights as they die. Don't have any down lights fortunately. Outside floodlights have already been replaced with LED floodlights.
Currently I use on average 30kw per day which is mostly at night as only my mother is at home during the day.
So what sort of usage,total watts per day, are you expecting from the system? You mentioned you want
20x65ah lead crystal batteries @ R2 500 each. batteries? By what I could see they are 12V batteries so how do you plan to configure them?
You would need to have 4 in series and then 5 parallel strings. Giving you 65ahx5=
325aH. From what I could gather on the interwebz is that people generally do not like having so many parallel strings. They all seem to recommend going with 2V batteries in series.
If you look at the link below having one day of backup power@17kw per day would require 17000 / 48V = 354aH@48V. At 85% storage efficiency that equates to at least
416aH required. And remember the inverter itself will use about (60W*24) = 1440W of power per day. So you effectively get 15560W.
Looking at the
Willard : RT 15 2V 445Ah battery you would need 24 of these @R2382x24=R57,168! So you need to spend +-R7000 more
NB.These calculations work in the assumption of 100% DOD. They recommend 50% max DOD. So you actually need to double the requirements as in the link example. The Willard RT25 762 A/H@R3000 seems like a better option then, which brings the price of the batteries to R74,000...
Although the led crystal batteries can be discharged 100% , I'm not really sure if they are meant to regularly?
I have not done any sort of ROI calculations but to me it seems that an off-grid solar solution might not be worth it. Since you would need to fork out R50-70k every 6 or so years for batteries.
My calculations might be wrong but to me it seems very expensive, a much better solution would be to feed back into the grid but that has all sort of regulatory issues at the moment.
Have a look at the
this.