Drunkard #1
Expert Member
- Joined
- Aug 15, 2007
- Messages
- 3,668
- Reaction score
- 18
Long story short: MY APC SURT UPS batteries failed and melted. In an effort to save the office from being burned to the ground when this happens again, we're completely changing the battery design and moving them outside. To design this properly, I needed to open the UPS. All batteries are connected to two poles on the main board, which leads to my question, "Is the design of these batteries seriously flawed?"
Obviously the ideal battery care situation is to have 96 x 2V cells individually monitored and charged. This isn't possible for such a small UPS. Next best would be individually monitoring and charging 16 x 12V batteries, and third choice being charging and monitoring the entire 16 x 12V string as one, which is what the UPS does if there are no external battery cabinets.
If there are external cabinets, they're just hooked up in parallel. So now (with one cabinet) you've got 3 parallel strings of 16 series-connected batteries. This causes parallel-series string interaction, and unless every battery is perfectly matched, melting batteries. I consider that a serious flaw.
Knowing this, I can't move the now spare battery cabinet to another site and just clip it in. Then I'd have 5 parallel strings with not-even-remotely matched batteries, and a 90% of a conflagration next time the power fails.
I find this quite disappointing. From thinking that these products were well designed to knowing they're flawed. Every new installation will now need a custom built battery bank if it needs more uptime than one string can provide. This is bull****, actually.
Have I missed anything? Electrical engineers, comments?
Obviously the ideal battery care situation is to have 96 x 2V cells individually monitored and charged. This isn't possible for such a small UPS. Next best would be individually monitoring and charging 16 x 12V batteries, and third choice being charging and monitoring the entire 16 x 12V string as one, which is what the UPS does if there are no external battery cabinets.
If there are external cabinets, they're just hooked up in parallel. So now (with one cabinet) you've got 3 parallel strings of 16 series-connected batteries. This causes parallel-series string interaction, and unless every battery is perfectly matched, melting batteries. I consider that a serious flaw.
Knowing this, I can't move the now spare battery cabinet to another site and just clip it in. Then I'd have 5 parallel strings with not-even-remotely matched batteries, and a 90% of a conflagration next time the power fails.
I find this quite disappointing. From thinking that these products were well designed to knowing they're flawed. Every new installation will now need a custom built battery bank if it needs more uptime than one string can provide. This is bull****, actually.
Have I missed anything? Electrical engineers, comments?