You need to add two things
1) Connect your Earth and Neutral together at the Axpert output (bridge earth and neutral).
2) You need to sink an earth pole into the ground. Generally a copper rod about 1.5 meters into ground and a wire running from that and connect to the earth of your Axpert.
Number 2 is because the stuff in your house are at earth potential. So you need to make sure you Axpert neutral and earth are both also at your local earth potential. Therefore if anything touches earth, it'll cause the current to "leak" and the EL to trip.
There's already an earth spike in the ground, with earth to the DB and the Axpert. I just wasn't sure of the Neutral-Earth bond, as many people said it shouldn't be done on the Axpert and can cause permanent damage.
Can anyone confirm that this works, without damage?