That is a TN-C-S install, sorry I thought you meant the panel in the house. That is a no-no.
Thanks Gnome. I guess the relay option would be the best then.
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
That is a TN-C-S install, sorry I thought you meant the panel in the house. That is a no-no.
One other thing that I wanted to ask... Is your inverter supplied by an E/L circuit, or directly from the "mains"?
One other thing that I wanted to ask... Is your inverter supplied by an E/L circuit, or directly from the "mains"?
No, it's direct.
Again, you are creating a dangerous circuit. Your earth wire to the inverter becomes a parallel conductor back to the Eskom transformer.
Electricity takes the path of least resistance. By paralleling you decrease resistance. Therefore, this new magical bond you've created will mean your home neutral and earth are sharing the neutral current back to the transformer. Bonded by your inverter wire.
You are connecting a wire between earth and neutral, the fact that it runs all the way to your inverter just makes it more dangerous. (and it is in contravention to SANS I should point out)
OK, so according to Gnome, that is incorrect.
Only if the earth-neutral bond is there when you are on eskom power. That is why we use a relay to only make the bond when running in battery mode. At that point there is no current flowing to/from the Eskom transformer.
OK, understood. So, if you are making the N-E bond on the inverter output, by means of the relay, while running in battery mode and you do have a E/L unit installed in-between the inverter output and the load supplied by the inverter, are you allowed to connect the inverter input to either before of after the main E/L unit? I know in your installation it is before, but is connecting it after the E/L also fine? Which one is the better/preferred option. What I'm after is the best way of connecting the inverter/ups both legally and safe.
Gnome, any comment?
Thanks guys!
Hi All
So here is what I found whilst testing....
In Battery Mode, during load scheduling, with your mains switch still ON, the Axpert will isolate the input neutral via its "safety relay" - see the image here: http://mybroadband.co.za/vb/showthr...-invertors?p=15835316&viewfull=1#post15835316
So the inverter's output neutral is only connected to the inverter.
So IMHO, the result of your test will be the same as turning the mains switch OFF - floating neutral on the inverter output.
Agreed, if that diagram is a block diagram of the Axpert's in question. That is why you have to bond N-E via the relay.
OK, understood. So, if you are making the N-E bond on the inverter output, by means of the relay, while running in battery mode and you do have a E/L unit installed in-between the inverter output and the load supplied by the inverter, are you allowed to connect the inverter input to either before of after the main E/L unit? I know in your installation it is before, but is connecting it after the E/L also fine? Which one is the better/preferred option. What I'm after is the best way of connecting the inverter/ups both legally and safe.
Gnome, any comment?
Thanks guys!
OK, understood. So, if you are making the N-E bond on the inverter output, by means of the relay, while running in battery mode and you do have a E/L unit installed in-between the inverter output and the load supplied by the inverter, are you allowed to connect the inverter input to either before of after the main E/L unit? I know in your installation it is before, but is connecting it after the E/L also fine? Which one is the better/preferred option. What I'm after is the best way of connecting the inverter/ups both legally and safe.
Gnome, any comment?
Thanks guys!
Okay so I cannot simulate load shedding because if you turn off the main double poll breaker you then are actually disconnecting the mains neutral from the inverter. So I have to wait for true load shedding so the neutral to mains is still connected.
If you are in Battery Mode, the relay is closed, causing the earth-neutral bond. When Eskom comes back ON, then the relay will open to remove the bond, but only after a finite (short) time. During that finite time, the E/L feeding the inverter input might see unbalanced neutral/live current, if the inverter draws power while the the additional bond is still in place. That will cause the E/L to trip.)
Check.The power going from your DB board to inverter can be VIA EL or without an EL. (The main EL used for your home)
Check.The power coming from your inverter should go through another EL.
Check.After an EL you can have many devices connected, so long as their neutral and live somehow end up being the neutral and live that goes VIA the EL.
You shouldn't create another path for that neutral or live to "skip" the EL.
Have had my APC 3000VA UPS connected after main E/L and running like that for more than 5 years and my infini connected the same and running for about 4 months without having any nuisance tripping though.Putting your Eskom -> Inveter power on the main EL might cause nuisance tripping for various reasons.
This is a bit confusing – how I understand this:This is how I connected my Inverter:
Main switch -> 25 amp circuit breaker & Eskom EL
So my Eskom EL is in parallel with the 25 amp breaker (my inverter is not on EL)
My output circuit breaker going to my Inverter is 25amp circuit breaker
My circuit breaker coming from the inverter is double poll 20amp circuit breaker with a EL
Here you refer to the main EL again.I'm using 4mm twin & earth
From there my main switch (Eskom) goes to an EL which is wired to various things in the home. (Stove, Geyser, 3 Plugs breakers)
Fine, incoming isolator labelled as Main (sub DB) – fed from Main DB. Check.The alternate power goes to various things (lights and two plugs).
At no point do I bond my Inverter and Eskom Neutral (they have seperate neutral connector strips).
At no point do I bond my Neutrals and Earth
At no point do I have a Live wire from my Inverter and Eskom to connect to the same circuit breaker (they are completely separate)
Additionally, right at the inverter I have:
A small DB box
Eskom power from panel running through a double poll isolator
Here you could have used a single pole breaker “feeding to the main DB”? Then on the Main DB, coming from the inverter, you’ll have to add another SP+N labelled something like “feed from inverter” and add a panel lamp to it to indicate that there is power coming from the inverter.Inverter power coming from Inverter running through double poll isolator (then goes to main panel).
Optional extra.Inverter output in parallel to isolator going to a surge protector. (DIN mount)
If you have a ground fault and both EL device are rated for 30mA (or less), it is luck of the draw which will trip.
Not only is it super annoying, it can actually mean that your Eskom EL will trip, switch to Inverter, then trip the inverter EL also. (Assuming you were running on Eskom power and the Eskom EL tripped first).
APC ups use center tapped transformer (at least my SUA1500i does). So they don't even tie the neutral and ground.Have had my APC 3000VA UPS connected after main E/L and running like that for more than 5 years and my infini connected the same and running for about 4 months without having any nuisance tripping though.
This is my current circuit:Eskom Main Switch supplies main EL and single pole CB feeding the inverter?
My inverter is not near my main DB, so right at the inverter I have a sub-panel with only an isolatorDouble pole isolator/trip/ EL combination on output of inverter?
Haha yes.Here you refer to the main EL again.Right?
YepFine, incoming isolator labelled as Main (sub DB) – fed from Main DB. Check.
The isolator is right at the inverter to turn off the inverter power. It isn't a circuit breaker. It is simply to isolate.Here you could have used a single pole breaker “feeding to the main DB”? Then on the Main DB, coming from the inverter, you’ll have to add another SP+N labelled something like “feed from inverter” and add a panel lamp to it to indicate that there is power coming from the inverter.
YepOptional extra.
Still waiting on it, but I'll probably just put it in the Inverter enclosure.What happened to the relay to sort out the Earth?
In my case my 3 phase Utility/Eskom EL trips first. It has higher sensitivity it seems.Yep, that happened a few times when I worked on circuits fed by the inverter and Neutral and Earth accidentally touched - Both EL devices tripped. (My inverter is connected after main EL)
Check.
Have had my APC 3000VA UPS connected after main E/L and running like that for more than 5 years and my infini connected the same and running for about 4 months without having any nuisance tripping though.
OK, so your installation is not 100% complete and obviously not CoC'd.Still waiting on it, but I'll probably just put it in the Inverter enclosure.
The SANS document says you should bond earth & neutral at the generator terminal.
I'm also not sure about the SANS requirements about putting such a relay in the sub-db, even if I have a DIN mount.