Pretty close to it yesSomething similar to this...
In your diagram you only need a Sub Main Switch (Double pole breaker) or a Isolator. Both aren't needed. You can do both if you feel so inclined
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
Pretty close to it yesSomething similar to this...
Pretty close to it yes
In your diagram you only need a Sub Main Switch (Double pole breaker) or a Isolator. Both aren't needed. You can do both if you feel so inclined
It is from a service manual for the Axpert (google: Axpert MKS-4000/KS-5000 Service manual)
If this is the correct block diagram for my inverter then my testing will prove the following.
Correct
- When the inverter is in bypass mode the double poll safety relay will be closed. This means that the Inverter AC output live and neutral are coming directly from mains. This means it is now currently bonded to the mains.
Correct
- However when the inverter is running on batteries the safety relay will be open thus the live and neutral from the mains are completely isolated from the inverter AC output. This is why the the neutral to earth on the inverter AC output shows a floating voltage. That means on battery power there is no neutral to earth bond at all.
Correct
- Taking into consideration that my lights and selected plugs will always be off grid and will always be isolated from the mains it implies that there is no bonding that can clash with the mains bonding. So in this situation bonding the AC inverter output neutral / earth makes sense.
Yes, no need for a “bonding” relay if the inverter will always be off-grid. Yes, do the N-E bond permanently.
- From the block diagram from what i can see you do not need or require a bonding relay and can bond the neutral to earth in the inverter DB panel.
Yes, an EL unit would be required, unless you run the inverter output to dedicated plug outlets.
- At the same time it would be wise to add an EL in the inverter DB panel for the plug circuits. Remember that I have moved my lights and selected plug breakers to the inverter DB Panel so they are completely isolated from the main DB panel.
Yes, if you have a (re-branded) Axpert 4KVA or 5KVA inverter.
Yes, an EL unit would be required, unless you run the inverter output to dedicated plug outlets.
If this is the correct block diagram for my inverter then my testing will prove the following.
- When the inverter is in bypass mode the double poll safety relay will be closed. This means that the Inverter AC output live and neutral are coming directly from mains. This means it is now currently bonded to the mains.
- However when the inverter is running on batteries the safety relay will be open thus the live and neutral from the mains are completely isolated from the inverter AC output. This is why the the neutral to earth on the inverter AC output shows a floating voltage. That means on battery power there is no neutral to earth bond at all.
- Taking into consideration that my lights and selected plugs will always be off grid and will always be isolated from the mains it implies that there is no bonding that can clash with the mains bonding. So in this situation bonding the AC inverter output neutral / earth makes sense.
- From the block diagram from what i can see you do not need or require a bonding relay and can bond the neutral to earth in the inverter DB panel.
- At the same time it would be wise to add an EL in the inverter DB panel for the plug circuits. Remember that I have moved my lights and selected plug breakers to the inverter DB Panel so they are completely isolated from the main DB panel.
So are you only going to use solar to charge your batteries? And you won't have any connection to your inverters 220V input?
No. There will still be a connection to the inverter AC input from mains. The reason for this is if the batteries are low and it is night time the MPPT built in charger will charge the batteries.
Also remember that if your load is to high for the batteries to run it it will also go into bypass mode so you do need the AC input to your inverter.
OK, but then your inverter is not off-grid and you cannot permanently connect the N & E and you will need the "bonding" relay.
When Eskom is on the relay will be powered and no N-E link will be created at the inverter output, but the N-E link before the main EL unit will be in the circuit as required.
Yes, but in all these cases Eskom is always on, so a simple Eskom-powered relay would always be powered, so neutral and earth would never be connected.
Yes, but in all these cases Eskom is always on, so a simple Eskom-powered relay would always be powered, so neutral and earth would never be connected.
The bonding relay needs to follow the internal bypass relay, which (if you have solar panels) depends on more than just if Eskom is present or not
Yes, but when the house is running off solar power the plugs won't be on that circuit
There is a better solution, namely using the 12v supply of the Inverter relay. That will work for all situations but requires modification which voids your warranty.
We were working on a solution here that does not involve anything too technical, doesn't void the warranty and works for most people in SA. Since most of us are using it as a UPS I think that is a decent solution
There is a better solution, namely using the 12v supply of the Inverter relay. That will work for all situations but requires modification which voids your warranty.
We were working on a solution here that does not involve anything too technical, doesn't void the warranty and works for most people in SA. Since most of us are using it as a UPS I think that is a decent solution
I have two lamps, one connected to Eskom, another connected to my alternate power.No visible leds when on inverter power ?
The relay option?Bit of an complicated option
Sense current on output
If output more than input bond neutral/earth
Yep, you don't see it that way?By "We were working on a solution here", do you refer to this thread?
To be fair, this thread is titled Axpert inverterI'm still stuck because I have an infini, which is a true hybrid, and I have PV panels installed as well. The infini combines PV power and Eskom to supply the load, no simple relay which switches between PV and Eskom to which I can connect a "bonding" relay.![]()
I just thought maybe "you and your colleagues at work" perhaps are working on a solution.Yep, you don't see it that way?
Point taken.To be fair, this thread is titled Axpert inverter![]()
constant power? Please explain. It works similar to the Axperts, but where the Axpert is not a true hybrid, the infini is. The infini can also grid-tie.Doesn't the infini require constant power from Eskom tho?
What I meant was if axpert have a visible led when on inverter you can use optic sensor to activate earth bond on output .I have two lamps, one connected to Eskom, another connected to my alternate power.
not following here tbh
Let me try again
Add current transformer on input (A)
Add current transformer on output (B)
Of current B is greater than A
Load must run off inverter connect the neutral earth bond