Our entire house is connected to a 8kw Sunsynk Inverter and a 5kw Battery. Neutral and Earth are bonded via the main DB board. Inverter is connected to main earth also in the main DB board.
Heated Towel rail in the bathroom has been shocking us (bare feet) and when I measured rit was producing 35v. It is connected to a single pole breaker (dedicated circuit) and when I turned this off the 35v was still there. Contacted the supplier and they sent a replacement element which has not fixed the issue.
Turn the Eskom supply off and this drops to about 5v
Sparky came round last night and after lots of testing and trouble shooting turns out the 35v is getting to the towel rail via the earth circuit from the inverter.
The supply and return from the inverter are earthed commonly within the inverter on the earthing point, these are then connected to the main earth point on the house. When this earth is removed from the inverter the 35v supply drops to about 11v and we can no longer feel the buzz on the towel rail.
We have temporarily disconnected the earth and then are contemplating running a dedicated earth spike just for the inverter.
Anyone else have an issue like this?
Heated Towel rail in the bathroom has been shocking us (bare feet) and when I measured rit was producing 35v. It is connected to a single pole breaker (dedicated circuit) and when I turned this off the 35v was still there. Contacted the supplier and they sent a replacement element which has not fixed the issue.
Turn the Eskom supply off and this drops to about 5v
Sparky came round last night and after lots of testing and trouble shooting turns out the 35v is getting to the towel rail via the earth circuit from the inverter.
The supply and return from the inverter are earthed commonly within the inverter on the earthing point, these are then connected to the main earth point on the house. When this earth is removed from the inverter the 35v supply drops to about 11v and we can no longer feel the buzz on the towel rail.
We have temporarily disconnected the earth and then are contemplating running a dedicated earth spike just for the inverter.
Anyone else have an issue like this?