You would need stands. Nothing much he could have done.So solar setup is installed. I don't know but I was hoping he would angle the panels a bit for better production and to make use of the bifacial panels but I will see later to optimize the setup a bit more.
So, the Navasolar Inverter even though it's in SUB mode it's still pulling from the battery. I need to go through the manual a bit more to understand exactly how this inverter will behave but so far when it was sunny I pull 4.5kw easy all via Solar and excess from battery/grid then the clouds rolled in. Ai
I mentioned yesterday that SUB and SBU does nothing. The inverter will pull from the battery until the cut off is hit and then switch to the grid. It unfortunately means limited savings if you dont have enough battery to last the night.
Can set the inverter to SOL, so that when it drains your battery to the cut off, it switches to the grid but only solar charges the battery. You would need to set the cut off a a SOC where if power goes, you still will be fine.